View Full Version : Pls, Help me! Chiller 30GX have alarm



tycon
11-01-2011, 09:54 AM
Hello everyone!
Chiller Carrier 30GX sometimes have alarm code 113 & 313: "Compressor A1 & B1 Star-Delta start-up failure". 02 Chillers has used 9 years old. They hadn't any privious that alarm. Althought,I replaced new SCPM board, new Contactors, new C.T... still happen it. Do anyone can help & give me the solution to solve that problem.
Notes: Chiller is modified to use the Motor Manager for each Compressor.3966

Gibbo
12-01-2011, 03:03 PM
As you don't seem to answer any of the guys questions suggest you get a carrier service engineer to site.

goshen
12-01-2011, 08:26 PM
Hello everyone!
Chiller Carrier 30GX sometimes have alarm code 113 & 313: "Compressor A1 & B1 Star-Delta start-up failure". 02 Chillers has used 9 years old. They hadn't any privious that alarm. Althought,I replaced new SCPM board, new Contactors, new C.T... still happen it. Do anyone can help & give me the solution to solve that problem.
Notes: Chiller is modified to use the Motor Manager for each Compressor.3966
Hi
you might want to check your control voltage supply
voltage drop could cause starter failure.
or possibly a faulty starter card!
good luck:D