15-08-2005, 02:49 PM
Can anyone assist by telling me the best way to flush a glycol system evaporator on a serveover counter to be used as a refrigerated one or can you get a small glycol unit to run just a counter


thanks

chemi-cool
15-08-2005, 07:44 PM
Hi JIMMYBOY.

Cleaning us simple but, is the coil can be used for refrigerant?
Or was it designed and made for water and glycol?
I would strongly advice you not to do it.
Get a new coil, designed for refrigerant

Chemi:)

Brian_UK
15-08-2005, 11:29 PM
JimmyBoy, welcome; if the systems has always run on glycol then I would assume that the pipework is NOT suitable for refrigerant - different grade of tubing and jointing.

It should be possible to get, or make, a small water cooler from which the chilled water could then be circulated around your existing coil.

JIMMYBOY
16-08-2005, 08:11 PM
everything looks good for gas just need best way of flushing and drying dont knopw if ofn would do

Brian_UK
16-08-2005, 10:54 PM
Well you could try a propriety tube cleaner followed by a set of triple evacuations to dry it afterwards.