View Full Version : McQuay Manuals
james10
08-01-2011, 06:51 PM
Hi All
i am after manuals for mcquay asl chillers if any one can help sorry for the lack of info it's all i have at the moment,
Thanks in advance
stufus
08-01-2011, 10:31 PM
James , this was posted here a while back may be of some use to you .
http://www.mcquay.ru/downloads/MTech%20II_sm.pdf
Cheers
Stu
james10
09-01-2011, 09:38 AM
cheers stu
D.D.KORANNE
11-01-2011, 08:31 AM
Thanks , useful stuff
camaro ss/rs
13-01-2011, 01:43 AM
Working on a wdc050 and looking to calibrate the evap pressure transducers.
camaro ss/rs
13-01-2011, 01:55 AM
Looking to calibrate the evap pressure transducers on a mcquay wdc 050. Can any one help out?
binti
13-01-2011, 01:06 PM
Looking to calibrate the evap pressure transducers on a mcquay wdc 050. Can any one help out?
I may be able to help (no promises) I haven't worked on a Mcquay centrif for a while so i may need some prompting.
what controller? Is it Carel with the touch screen and swing out arm? Or older on microtech? (true microtech not re-badged carel)
What sections of the soft ware can you access? I can't remember where the calibration section is but i do have most of the passwords and manuals in boxes in the garage.
Also how far out of calibration is the transducer? If it is a fair way out i would suggest you simply replace it.
camaro ss/rs
18-01-2011, 10:27 PM
Hi Binti. Thanks for the reply. New to this site and to Mcquay chillers. This wdc050 has a swing out display and a micro tech 2. I found that some person put an offset on the evap and cond pressure transducers. I tried putting the password into the swing out display and that allowed me to change the offsets and to calibrate the press transducers. All ok at this time.:rolleyes:
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.