had one of these faulty,found the power element u/s the valve was 4 ton capacity,however in my stock i had a 1 ton valve so i removed the element from the good valve,now they are both on the same refrigerant r22,the question is will it work?

Brian_UK
15-12-2010, 07:25 PM
If the power head is the same then why not?

monkey spanners
15-12-2010, 07:37 PM
Yeah, they are the same, KT43 VC if my memory is correct. Fit a lot of them on Fabdec milk tanks as the chemical fumes in the dairy rots them out!

cadwaladr
15-12-2010, 08:53 PM
thanks guys i thought as much

Mr-Frosty
15-12-2010, 09:35 PM
as long as the valve bodys and gaskets match up and you use the correct orifice for the purpose or set the orifice correctly there will be no problem whatsoever.