Brian808
02-12-2010, 08:20 PM
Hi All,
I have a custom built water cooled package unit made by Energylabs (I've always had issues with this manufacturer)....2 screw compressors, interlaced evaporator, condenser water reheat coil, powered by a ALC system. The problem I'm having is the evaporator condensation is getting sucked off the coil past the drain pan and onto the reheat coil and leaking from the bottom of the unit. This is a draw through system. Ducted supply and return, The filters and coils are very clean, outside air is balanced to code (thought there was to much humidity going into the system being from Hawaii) it just seems like there is too much condensation. The system was working fine for about 4 months and this just popped up. I'm assuming it's due to only one circuit running? And the evap coil isn't getting "cold" enough. Anyone have any other ideas???
Thanks
I have a custom built water cooled package unit made by Energylabs (I've always had issues with this manufacturer)....2 screw compressors, interlaced evaporator, condenser water reheat coil, powered by a ALC system. The problem I'm having is the evaporator condensation is getting sucked off the coil past the drain pan and onto the reheat coil and leaking from the bottom of the unit. This is a draw through system. Ducted supply and return, The filters and coils are very clean, outside air is balanced to code (thought there was to much humidity going into the system being from Hawaii) it just seems like there is too much condensation. The system was working fine for about 4 months and this just popped up. I'm assuming it's due to only one circuit running? And the evap coil isn't getting "cold" enough. Anyone have any other ideas???