View Full Version : Need for Glycol



Hemant Anand
23-07-2005, 11:02 AM
We are replacing our ice water system with a chilled water system. The supplier says we have to use glycol since temp is 2C. Upto what temperature can we operate this R22 based system without using any glycol. Is 4-5C OK? :confused:

dill
23-07-2005, 12:02 PM
welcome hemant, in the office building I look after we use large flooded systems using r22. the chilled water flow temp is set for 6 degrees centergrade. We have had it down to 5 degrees but any lower and we run the risk of bursting the tubes. remember the temperature in the evaporator will be lower than the leaving temperature of the water so I would be cautious about running a water chiller any lower than 4 or 5 degrees.

frank
24-07-2005, 01:53 PM
I would be cautious about running a water chiller any lower than 4 or 5 degrees.

Hi Dill

I think you meant without using glycol. :)

TXiceman
24-07-2005, 11:10 PM
Conventional design says that 4.5 dC (preferred is 5 dC) is the lower limit for normal shell and tube design chilers. Special chillers are desingned which can get the LWT down to about 2 dC or a bit lower. One of this type is manufactured by Chester Jenson or Mueller Co. in the US. One name for this type chiller is a sliding film type.

Ken

Hemant Anand
03-08-2005, 01:41 PM
Conventional design says that 4.5 dC (preferred is 5 dC) is the lower limit for normal shell and tube design chilers. Special chillers are desingned which can get the LWT down to about 2 dC or a bit lower. One of this type is manufactured by Chester Jenson or Mueller Co. in the US. One name for this type chiller is a sliding film type.

Ken
Thanks a lot.

shooter
15-08-2005, 08:15 AM
yes 4 degrees is possible with a good flow over in the tubes.
if the r22 is inside the tubes you can go deeper as the ice will build around the tubes.
why do you need to go lower?
and if you need 0 why not use ice slurry
at sea we make the slurry and it is nice 0 with some seawater around it.