View Full Version : Alarm 56 in Chiller Carrier 30RA
tambymah
11-11-2010, 10:15 AM
Hi all,
I have faced the Alarm 56 in Chiller Carrier 30RA, but whe I look up in the catalog I find nothing about this Alarm.
Please advise.
Thanks in advance.
Tamby
Syria
00963955978515
acnerd
11-11-2010, 01:07 PM
If you go into the alarm history menu on the chiller itself, it should tell you what the alarm is?
james10
11-11-2010, 05:53 PM
when displaying the fault press enter and the alarm description will be displayed
hoodemar
12-11-2010, 07:36 AM
It can be the reason for ur unit.
"Excessive temperature in the
control box "
if not pls write the full model number
Gibbo
13-11-2010, 08:28 AM
There are 2 versions of this chiller version A has alarm 56 and version B does not. You probably have the wrong manual.
Willem V
13-11-2010, 11:47 AM
you're sure it's a 30RA and not a 30RB for example, do you've the exact type and year of make?
Willem V
13-11-2010, 06:26 PM
Gibbo was wright, it's in 30RA version A, and means:
Excessive temperature in the
control box (only for “Option 16”
units)
Willem V
13-11-2010, 06:30 PM
and option 16 is high ambiant version
Willem V
13-11-2010, 06:32 PM