Had a call to a PARF27 controller group not heating today.
When switched to heating, the controller went into standby (as normal) but instead of bringing on the heating reverted back to cooling mode.
Investigated the G50 and found none of the groups had been assigned their corresponding PARF27 address.
Made the necessary changes, checked heating to cooling and back again and all fine - BUT -
I installed and commissioned this site a couple of years ago, it's 27 cassetts interlocked with Lossnays and there has been no problem until today.
Nobody has tampered with the G50, it's locked in a cupboard!
Can anyone explain why the G50 lost its PARF27 addresses and why only the one controller/group was playing up.
Could this be a software fault with the G50? :rolleyes: