View Full Version : frick RXF-39H



serviceman
04-11-2010, 08:52 PM
I had problems with the oil temperature of this equipment is a system that uses ammonia and serves as a chiller I leave the machine operating data before protected.

100% capacity
2.20 volume
37.5 psig suction pressure
temperature 10.8 ° C
15.4 ° C superheat

133.4 psig discharge pressure
temperature 86.2 ° c
60.6 ° C superheat
oil pressure 130 psig
temperature 73.7 ° c

process temperature 11.5 ° C
10.0 ° C setpoint
12.0 ° c boot
unemployment 9.0 ° c

I hope their comments and their help

ping
05-11-2010, 12:17 AM
hi, you have too high suction superheat, try to less it.

charlie n
05-11-2010, 09:45 AM
Agree with ping. If this is a flooded chiller the superheat should be almost 0. What is the oil cooling method?

serviceman
05-11-2010, 02:14 PM
oil cooling is liquid (eazycool), the evaporator is flooded and even goes ahy heat exchanger

That's too cold
16-11-2010, 06:02 PM
What is the oil high temp set point?

serviceman
23-11-2010, 03:00 PM
167°f cout uot hig oil temp

josef
23-11-2010, 04:22 PM
Can Cooler - ammonia with oil? compressor is in good condition? does not vibrate? noise?

serviceman
23-11-2010, 05:16 PM
josef
the compressor is new, operating at 100% increases the temperature, ammonia, oil is cooled by liquid injection, and the evaporator is flooded, we used as chiller

josef
23-11-2010, 05:40 PM
Insuffi cient liquid supply. Check receiver level. Check strainer.
Suction superheat too high. Correct system problem.
Liquid strainer blocked. Clean strainer.
Operating conditions signifi cantly different from design.
Malfunctioning Vi Control Solenoids. See function check of the compressor
"Volumizer II Vi Control" for further detail.
Check motor valve operation and calibration.
Check calibration of analog output.

serviceman
23-11-2010, 06:59 PM
ok, the calibration of the valve and was verified, the correct operating saw and automatic way, I amtenido the compressor at 85% capacity and works well, the liquid level is 3 peephole in the entrance of liquid and 2 in the evaporator

josef
23-11-2010, 07:51 PM
Volume goes 2.2 to 5?

serviceman
23-11-2010, 08:13 PM
yes. cleaning strainer succion,liquid inyection.return oi strainer

serviceman
23-11-2010, 08:15 PM
are in fact three compressors Frick and only protects the new

josef
23-11-2010, 09:58 PM
Check your email

serviceman
23-11-2010, 10:21 PM
josef:

thanks

Magoo
23-11-2010, 11:06 PM
The liquid injection is too low, check expansion control and receiver supply levels.

serviceman
24-11-2010, 02:37 PM
the injection of liquid is a electronic valve

josef
24-11-2010, 03:10 PM
The compressor is new or overhaul?
I think your problem is the compressor.

serviceman
24-11-2010, 07:30 PM
compressor is new.lo've been working at 90% maximum load

RANGER1
24-11-2010, 08:17 PM
serviceman ,
If you have liquid injection discharge temp & oil temp should be same .
What is the liquid injection set point ?
I would have thought between 130 -140 f .
Sensor should be on ideally discharge line out of compressor .

As everyone also suggests good liquid reciever levels.
Also oil injection into rotors must be adequate to assist cooling of compressor as not enough may cause rotor damage .

josef
24-11-2010, 08:45 PM
Thank serviceman, so you have a compressor problem. Calibration, capacity control, perhaps from the production.

serviceman
13-01-2011, 03:46 PM
thanks josef

josef
13-01-2011, 10:07 PM
Do not write more?

CanadianIce
17-01-2011, 04:57 PM
Have you verified that the main oil injection orifice is the correct size? Sounds like the orifice is too small. Frick usually sends a package of different sized orifices with new compressors. I've had to change several of these.

C Ice

serviceman
17-01-2011, 05:51 PM
When the package arrived only brought hand cooling, oil filter and oil. holes will have a picture?

Mark Selby
25-04-2011, 05:11 PM
There is a 7 turn valve that should have a yellow cap on it. If that valve is not set correctly that could also affect your oil and discharge temps