View Full Version : elliwell controller
martin99
19-10-2010, 07:57 PM
:rolleyes:I have an elliwell ewts 12 defrost controller, i know how to adjust the interval time but can i set it so it does not go into defrost at all ?
chemi-cool
19-10-2010, 08:35 PM
Isn't it electronic timer?
martin99
19-10-2010, 08:40 PM
Yes it is.
chemi-cool
19-10-2010, 09:12 PM
OK, Go to Eliwell web site and look for ewts, there are a few of them, see which one is the one you need.
Grizzly
19-10-2010, 09:40 PM
Hi Martin.
I cannot find any reference to a EWTS 12 only a 72.
Within the details I can find there is reference to a defrost end temp range of 3-15c.
I suspect your operating temps are below this, otherwise why would you need a defrost!
You could install a switch in line with the defrost output.. Terminal 8.
Which would negate any defrost settings. (but maybe not the fan control)?
These may need there output switching too?
Because there does not appear to any means of electronically overriding this controller.
Short of powering it down?
Why do you need to override it?
Grizzly
goshen
20-10-2010, 06:00 AM
:rolleyes:I have an elliwell ewts 12 defrost controller, i know how to adjust the interval time but can i set it so it does not go into defrost at all ?
http://www.srw.co.uk/pdf/Eliwell/EWTS%2070%201.98%20ing.pdf
see if this is of any help:D
Grizzly
20-10-2010, 06:52 AM
Hi Martin.
If the 70 model Chemi has posted above, is similar.
You may well Be able to control the defrost.
Using the Klixon control method and switching across terminals 3&4.
Good luck Grizzly.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.