View Full Version : Over Condensing????
gazzza
16-09-2010, 11:22 AM
Who is teaching our poor apprentices this term? I have been a refrigeration mechanic in NZ and OZ and still hear the same thing from people. The system is "Over Condensing" It drives me crazy and doesn't even make any sense. Is this just a cop out for people who don't understand sub cooling?
If i am wrong can some one else please explain?
nike123
16-09-2010, 11:42 AM
http://www.refrigeration-engineer.com/forums/showthread.php?t=13857
NoNickName
16-09-2010, 11:51 AM
A little bit like "overkilling". Once one is dead, can't be killed further.
Grizzly
16-09-2010, 06:06 PM
It's sad that you feel that if someone uses the term "over condensing" they are not correct.
I have first hand experience of chillers that have to much "Sub cooling" the politically correct answer maybe.
Either way when an "over condensing" situation does occur.
You loose your Head Pressure control, the "lift" across the Comp.
To low suction pressures can occur and a whole Host of related issues.
OK it's not actually possible to over "Sub Cool" refrigerant.
Surely it's more important than we all understand what is meant?
It's like you get Receiver, reclaim and recovery cylinders.
Just terminology really!
Grizzly
paul_h
16-09-2010, 07:08 PM
Who is teaching our poor apprentices this term? I have been a refrigeration mechanic in NZ and OZ and still hear the same thing from people. The system is "Over Condensing" It drives me crazy and doesn't even make any sense. Is this just a cop out for people who don't understand sub cooling?
If i am wrong can some one else please explain?
I use the term when the condenser is cooler than the rest of the liquid line, causing the liquid refrigerant to turn into vapour again before the liquid flow control device.
It's a real thing you can see in systems with a sightglass before the TX. IE you can measure subcooling after the condenser, but if it's a remote condenser, what happens between it and the remote receiver and TXV?
No point adjusting refrigerant level or TXV setting until you ascertain whether the system may be 'over condensing'
I don't know where you are tackling this problem or name from, but it's a real thing, thats why systems have HP fan control, variable speed fan control, or fans come on in stages etc. If the condenser is too cool, you'll get 'over condensing', ie any liquid from the condenser unstable and will boil off when leaving a cold condenser and going to a warm liquid line.
NoNickName
16-09-2010, 07:39 PM
will boil off when leaving a cold condenser and going to a warm liquid line.
How is it possible the liquid line warmer than the condenser? Would you please explain to me such scenario?
Discharge
16-09-2010, 10:05 PM
Subcooling and over cond. do not go hand and hand. if your over cond. then your wasting energey. it helps to keep a constent pressure on your txv's. If your over cond. than you may be loging refrigerent in the condensor, giving the false impression that your low on gas.
monkey spanners
16-09-2010, 10:39 PM
How is it possible the liquid line warmer than the condenser? Would you please explain to me such scenario?
Condensing unit out side in winter running a coldroom in a kitchen, the liquid line section in the kitchen will be above the outside temperature.
Liquid line should be insulated in such conditions.
Jon :)
lowcool
17-09-2010, 02:43 AM
gazza you sound like your undercondensing.if your condensing pressure is lower than the designed system rated pressure then it is over condensed
NoNickName
17-09-2010, 07:39 AM
Liquid line should be insulated in such conditions.
That's a unique scenario, and IMHO unlikely. In a controlled condensation, the fan speed in such low ambient will be almost or if not at all OFF.
Liquid will still be warm enough, to avoid such situation, unless a IHE between suction and liquid is installed.
That's more credible. Suction at -20, liquid leaving condenser at 30°C, liquid entering receiver 0°C.
TRASH101
17-09-2010, 09:16 AM
I am having trouble with some of the interpretations of "over condensing" and "excessive sub cooling"
If, by definition, over condensing means more liquid is formed by condensation than what is anticipated by normal design parameters then it most certainly does exist when the design parameters are exceded by fault or other.
Excessive sub cooling is a very real concern for proper operation of most expansion devices (both in pressure drop and ability to actively control superheat)
They are both very close in definition but with over condensing there doesn't have to be a significant amount of sub cooling.
mad fridgie
17-09-2010, 09:38 AM
There is no such thing as over condensing, what there is; to lower liquid pressure to ensure correct refrigerant mass flow through the evap at a said condtion, and has nothing to do with sub cooling (which is not going to happen at the outlet of the reciever)
TRASH101
17-09-2010, 01:29 PM
There is no such thing as over condensing
Why not???
I'snt it correct that, in a thermodynamically balanced state, any change in the physical variables (namely the thermo physical effects on the high side heat exchanger) on a running system will change the proportional volume of liquid to vapor? Is the liquid not condensate (i.e. the product of the process condensing)?
If the above is true then any change to the ratio of liquid to vapor volume past its design must be considered as under or over condensing respectively.
I submit my postulation for your intrest/ amusement/ ridicule.;)
I have to agree with mad fridgie's view. Here's my take.
If additional condensation occurs, then for thermodynamic equilibrium to exist in the cycle, something else must alter to balance the first law of thermodynamics. The evap will then try to balance itself by moving (downwards if cond pressure reduces) on the log(p)-h chart such that Q'evap + W'comp = Q'cond. The evap will then probably run too cold. In other words, the cycle will 'float' downwards.
Controlling the hp end to run where preferable, will 'peg' the cycle to stay where desired.
TRASH101
17-09-2010, 04:02 PM
If additional condensation occurs, then for thermodynamic equilibrium to exist in the cycle, something else must alter to balance the first law of thermodynamics.
Hi Des
The above doesn't agree with mads' statement
There is no such thing as over condensing
I agree that it will achieve a balance to whatever the new conditions but if that equilibrium is not the desired condition then that shift has still been caused by a proportional shift in the liquid/vapor ratio which if viewed as a function of the condenser then it could be described as over condensing.
I hasten to add that I agree that the term over condensing is used by others as a " can't be ar5ed to tell you whats wrong " or " I really don't know what is wrong with it " statement but in its purest defined state it does happen and when it does it is invariabley a fault in the system or the system is being used outside of its design parameters.
NoNickName
17-09-2010, 04:12 PM
Overcondensing doesn't exist. A variation in the titration of vapor to liquid happens at constant T and P in the 2-phase equlibrium.
In looking through the definitions offered, it seems the term "overcondensing" does not accurately describe the problem.
Being from the old school, we used to call this "low head pressure", although "liquid underfeed" would be more descriptive.
Personally, I prefer terminology that actually describes the problem and overcondensing doesn't accurately describe anything. If anything, it is misleading. You can't overcondense.
NoNickName
17-09-2010, 04:45 PM
Agreed with Gary. Let's put this to rest.
shieldcracker
17-09-2010, 05:26 PM
Why not???
I'snt it correct that, in a thermodynamically balanced state, any change in the physical variables (namely the thermo physical effects on the high side heat exchanger) on a running system will change the proportional volume of liquid to vapor? Is the liquid not condensate (i.e. the product of the process condensing)?
If the above is true then any change to the ratio of liquid to vapor volume past its design must be considered as under or over condensing respectively.
I submit my postulation for your intrest/ amusement/ ridicule.;)
Condensation means a change in state from gas to liquid. Over condensation would mean having excess of condensate (liquid refrigerant) period. You can have an excess of liquid refrigerant in the condenser and this is better described as flooded condenser or flooded operation, so essentially the level of liquid in a condensing coil will determine the volume ratio of vapor to liquid. There is no design parameter that fixes the volume of vapor to liquid refrigerant in the condenser, this is a dynamic point in the condenser operation that changes with the operating conditions of the equipment.
Over condensation would imply that one could achieve different rates of condensation from a substance in vapor state which is impossible. The rate of condensation formation is fixed for a given set of state variables.
I hope this clarifies things.
nevgee
17-09-2010, 10:09 PM
If you are, you breathe. If you breathe, you talk. If you talk, you ask. If you ask, you think. If you think, you search. If you search, you experience. If you experience, you learn. If you learn, you grow. If you grow, you wish. If you wish, you find. And if you find, you doubt. If you doubt, you question. If you question, you understand and if you understand, you know. If you know, you want to know more. If you want to know more, you are alive.
Does this just mean "I think therefore I am" ?:)
Grizzly
17-09-2010, 10:42 PM
OK. So the purists have explained why I cannot use the term "over condensing!"
OK so I can only get a finite amount of vapour or liquid refrigerant.
My dilemmas usually occur when that Liquid is at a lower temperature than normal.
IE, its a cold windy night and the system temps at standstill (Duty satisfied).
The system starts up but because of the low H.P. side temps/ pressures and therefor the low LP temps/pressures.
The system trips, a common enough occurrence.
Particularly with Chiller packs.
I until now, (for I have been converted from using such terminology).
Would of referred to the system as over condensing!!
So for this situation where there is to little heat in a system.
What do people suggest I use as viable Terminology?
Grizzly
mikeref
17-09-2010, 11:36 PM
I have to agree with Paul H, though i see where the term does not make sense. Here's my view.Given any working system. Evaporator absorbs heat, condenser rejects heat. Balance achieved.Condenser fails to reject required heat removal, discharge pressure rises, high temperature liquid/vapour supplied to evaporator,.. undercondensing. Back to "balanced" opperation, now the ambient is lower but all condenser fans are running so the condenser completes heat rejection more efficiently, now liquid is being subcooled where vapour was previously condensing,vapour volume is less, discharge pressure falls, suction pressure drops, it seems the equipment is running short of refrigerant, cool liquid line with liquid/vapour mix. This is my defination of "overcondensing".. mike.
monkey spanners
17-09-2010, 11:50 PM
Its just a term for a condition!
Overcondensing = too low a head pressure, its just a word so we know whats wrong. Its simple so the customer can grasp the idea.
Often i have to call a condenser a radiator so that people know which part i'm on about.
Some call a spade a spade, some call it a metal bladed digging implement with a beech wood shaft.
Language is just a tool like any other, so long as people understand what we want to comunicate it has served its purpose.
Jon :)
nike123
18-09-2010, 12:10 AM
Does this just mean "I think therefore I am" ?:)
In short, yes.
I know lot of zombies around me.;)
nike123
18-09-2010, 12:13 AM
Language is just a tool like any other, so long as people understand what we want to comunicate it has served its purpose.
Jon :)
That is why I like German word sausages. They are usually explanation by itself.:D
That is why I like German word sausages. They are usually explanation by itself.:D
Sausage condensing? :confused:
nike123
18-09-2010, 07:51 AM
Sausage condensing? :confused:
:D
You need example?
;)
Donaudampfschiffahrtselektrizitätenhauptbetriebswerkbauunterbeamtengesellschaft
"association of subordinate officials of the head office management of the Danube steamboat electrical services"
NoNickName
18-09-2010, 11:31 AM
What do people suggest I use as viable Terminology?
Poor engineering.
Grizzly
18-09-2010, 12:58 PM
Poor engineering.
????
Pardon?
Grizzly
Quality
18-09-2010, 01:09 PM
A little bit like "overkilling". Once one is dead, can't be killed further.
You want to try my wife's cooking:D:D:D
paul_h
18-09-2010, 05:49 PM
That's a unique scenario, and IMHO unlikely. In a controlled condensation, the fan speed in such low ambient will be almost or if not at all OFF.
Such a perfect world you live in. Some of us have to deal with domestics, static, and cheap units.
If this term "over condensing" doesn't exist because theres fan control, what do you call the conditions that exist when there's no fan control?
Do you call it fiction and say it can't exist just because you believe there's no such system in the world without condenser pressure control?
It's fair to call it another name, or to explain it is something else. But to say it can't happen because you live in an insulated world where you don't see it is ridiculous. Same goes with charging liquid into the suction service valve, it happens all the time because there is no choice.
It happens and is out there because things are built and designed to budget and repaired to budget and compromises and the like are made.
I know we are worlds apart, and you can run rings around me as far as engineering and large systems. I'm not trying to insult, I've worked on large systems though for not a such a long time. I specialised in small systems in order to get self employed. Pauls big industrial refrigeration company wasn't ever going to get of the ground with just me and pocket change, so I've kept with the small stuff to keep me busy. If I ever close shop, and I'm pretty close because I hate constant phone calls etc, yeah I'd like to work more on the industrial side as an employee. But there is completely different conditions, expectations and reality down here - not referring to geographical location either.
NoNickName
18-09-2010, 05:57 PM
I didn't say poor engineering doesn't exist. Surely overcondensing doesn't exist.
For what it's worth, a pressure switch connected the fan conctactor costs few euro or gbp or aud. Face it: fixing a unit requires some dedication.
paul_h
18-09-2010, 06:12 PM
I didn't say poor engineering doesn't exist. Surely overcondensing doesn't exist.
For what it's worth, a pressure switch connected the fan conctactor costs few euro or gbp or aud. Face it: fixing a unit requires some dedication.
wow, just wow.
A thought could be to describe the phenomenon on the log(p)-h chart & then detail what is actually occurring in this situation.
monkey spanners
18-09-2010, 06:56 PM
I didn't say poor engineering doesn't exist. Surely overcondensing doesn't exist.
For what it's worth, a pressure switch connected the fan conctactor costs few euro or gbp or aud. Face it: fixing a unit requires some dedication.
Fixing a unit does require dedication, something that is not lacking in the posters on this forum, but out on site it also requires payment for the parts and time, and for this you need the customers permission to carry out the work. Simple economics.
One of my jobs on friday was a milk cooling tank water pump replacement, it should have three pumps but only had two and one of them had failed causing over £1000 worth of milk to spoil, yet the customer wouldn't have a third fitted...
The condensing unit was also covered in milking vacuum pump oil as the exhaust blew directly onto it, i adviced them the system needs a service and clean, this again was declined.
Many customer run equipment on a FOF principal (fix on fail) and don't care so long as the machine is making a noise.
Why not see if you can spend some time working with an engineer out and about servicing stuff, i know you know your stuff with the equipment, but i'm sure it would be a usefull experience with regard to customers and operators of plant.
Jon :)
The words - rock & hard place, come to mind.
NoNickName
18-09-2010, 08:20 PM
Many customer run equipment on a FOF principal (fix on fail) and don't care so long as the machine is making a noise.
Sorry for being direct and brutal, but fitting a pressure switch for keeping the condensing pressure high enough to avoid low pressure alarms doesn't involve any of these wasted arguments of yours.
Actually, I think that refrigeration engineers prefer to have themselves payed (read: overpayed) for charging refrigerant than actually spending some time and brain to repair units and fix the problems once and for all.
Then, they come here and whine like sissies about "overcondensing" except that such phenomenon doesn't exist anywhere else than in their huge ignorance.
Grizzly
18-09-2010, 08:51 PM
Sorry for being direct and brutal, but fitting a pressure switch for keeping the condensing pressure high enough to avoid low pressure alarms doesn't involve any of these wasted arguments of yours.
Actually, I think that refrigeration engineers prefer to have themselves payed (read: over-payed) for charging refrigerant than actually spending some time and brain to repair units and fix the problems once and for all.
Then, they come here and whine like sissies about "overcondensing" except that such phenomenon doesn't exist anywhere else than in their huge ignorance.
Do you insult everyone that disagrees with you?
Because you certainly seem to do so a lot on this forum.
You are only reading what you want to on this post.
I have accepted that the terminology is wrong!
Along with many others.
And any form of pre-set pressure control is irrelevant when the system fails to reach it.
Or is that down to poor engineering?
I am willing to accept many of your comments but why such a bitter answer?
Grizzly
r.bartlett
18-09-2010, 10:32 PM
Years ago we would often get called to look at a split in the winter which running on cooling had the indoor unit iced up solid. We called that over condensing and when we blocked the 'radiator' the suction would come up to 60 psi and not ice again.
So I have used the term 'over condensing' with reference to this particular problem way back in the early eighties and I shall continue to do so. And if someone stands there and say's "Oh I think you'll find it's called excessive sub coolarghhhhhhhhhh"*thud*
That was me throwing him off the roof for being such a bellend :D
monkey spanners
18-09-2010, 10:33 PM
Sorry for being direct and brutal....
Then, they come here and whine like sissies about "overcondensing" except that such phenomenon doesn't exist anywhere else than in their huge ignorance.
Being direct and brutal can be a kindness if it is done with compassion and with the intent to help another being, if not it serves only to boost the ego then why be direct and brutal if it has potential to hurt another?
I'm not whining, i am sorry if you percieve me that way, i had a similar reaction to the term the first time i heard it years ago, "how can a system overcondense?" but realised it is just a word and nothing that important to get upset about.
I have never claimed to be anything but ignorant, it is one of the reasons i visit this site to learn from the many members here, yourself included.
Jon :)
r.bartlett
18-09-2010, 10:38 PM
If you are, you breathe. If you breathe, you talk. If you talk, you ask. If you ask, you think. If you think, you search. If you search, you experience. If you experience, you learn. If you learn, you grow. If you grow, you wish. If you wish, you find. And if you find, you doubt. If you doubt, you question. If you question, you understand and if you understand, you know. If you know, you want to know more. If you want to know more, you are alive.
Does this just mean "I think therefore I am" ?:)
I'm a small tin of spiced ham "I'm pink therefore I'm spam":cool:
750 Valve
19-09-2010, 08:05 AM
Sorry for being direct and brutal, but fitting a pressure switch for keeping the condensing pressure high enough to avoid low pressure alarms doesn't involve any of these wasted arguments of yours.
Actually, I think that refrigeration engineers prefer to have themselves payed (read: overpayed) for charging refrigerant than actually spending some time and brain to repair units and fix the problems once and for all.
Then, they come here and whine like sissies about "overcondensing" except that such phenomenon doesn't exist anywhere else than in their huge ignorance.
I cannot believe the absolute drivel you have posted in this thread, you are taking a tunnel visioned stance based on two words "over" and "condensing".
The situation exists in so many systems across the world (except quite clearly Merate (LC) Italy! which must something akin to a thermodynamic Utopia) and it does not matter what people call it, the fact remains that under much colder than design ambients where systems that have remote condensers operating quite a bit colder than both the system receivers and liquid lines that this phenomena can occur.
In Australia we have to engineer for ambients such as 40C during summer, those same systems can operate at -7C ambient during winter - this brings about challenges in maintaining an achievable operating envelope, say for instance in supermarkets we have remote condensers operating at ambient conditions, plantrooms containing the rack and receiver can be anywhere from ambient temp to conditioned air temps - I am sure someone just wanting to win an argument (which is how No Nickname is coming across) will say engineering dictates that we should place the receiver at the condensers in the ambient air to stop "over condensing", the same genious should also think of the affects this has at max design conditions..... yes - less than desirable isn't it?? So lets insulate the receiver then.... what does this do in summer at design max??? Yes it hinders natural subcooling doesn't it?
To overcome issues we cycle fans and/or run variable speed drives however even with fan cycling you can observe issues in low ambients as a fan cycles on and changes subcooling conditions dramatically. A genius engineer would say just use smaller fans and more of them to alleviate the effect, or even 6 or 8 pole fan motors.... there is a commercial reality we must all adhere to and at the end off the day we are left with less than perfect systems, it is our job to get the best out of them under all conditions.
So when someone comes on here whining about over condensing - my advice to you Mr No Nickname is to just look at another thread, don't let a technician trying to make a system operate better get under your skin, just make a conscious decision not to help him and go back to your thermodynamic Utopia and be happy you don't have to deal with any less than desirable design and operating conditions.
END RANT :rolleyes:
mad fridgie
19-09-2010, 09:20 AM
The OP did ask about teaching, so a correct description, had to be given!
As monkey said we all use the term over condensing, instead of saying the condensor is oversized, which leads to reduced discharge pressures, this is not be confused with liquid sub-cooling, which completly different. Best engineering is always easy when money is not important, but in these hard times, you look at cost all of the time, do you think the client understands, no he just sees the money and listens to the salemen. The practrical implecations are that we cut corners which are going to give the biggest ruduction cost with minimal risk on reliability, normally at the cost of efficiency and product quality (lower sst, for example dries out fresh product)
NoNickName
19-09-2010, 09:55 AM
I don't agree a single word of the rants above. I'm much more used to watch refrigeration engineers (around the world) temporarily fixing the issues with their system to guarantee more problems for the next month to come, and ensure bread and butter for themselves as seasons change.
The overcondensing thing, once again as other posters already stated, doesn't exist. There's no overcondensing whatsoever.
And for what it's worth, there are plenty of systems that all year long experience a range of temperatures much larger than australians.
I install and maintain condensing units in siberia, with 30°C in summer and -50°C in winter. How would you call that: hypercondensing?
Do you happen to know that almost all refrigerants at -50°C is liquid at atmospheric pressure, so that you don't even need a recovery unit for recovering it?
But then again, please go ahead with rants on cutting corners, price driven projects, cost reduction and bla blah.
mad fridgie
19-09-2010, 10:30 AM
I don't agree a single word of the rants above. I'm much more used to watch refrigeration engineers (around the world) temporarily fixing the issues with their system to guarantee more problems for the next month to come, and ensure bread and butter for themselves as seasons change.
The overcondensing thing, once again as other posters already stated, doesn't exist. There's no overcondensing whatsoever.
And for what it's worth, there are plenty of systems that all year long experience a range of temperatures much larger than australians.
I install and maintain condensing units in siberia, with 30°C in summer and -50°C in winter. How would you call that: hypercondensing?
Do you happen to know that almost all refrigerants at -50°C is liquid at atmospheric pressure, so that you don't even need a recovery unit for recovering it?
But then again, please go ahead with rants on cutting corners, price driven projects, cost reduction and bla blah.
I do not agree with your statement on bread and butter, although I do believe that many do not understand why they do, what they do, but it works for them. but that is not the same as intentionally ripping the clients.
Hypercondensing, lol
the rest, well that just depends which world you live in. I too was perfect, then I woke up!!!!!!!!!!!
How to optmise hypercondensation & negate it's downside potential?
;)
Quality
19-09-2010, 02:08 PM
How to optmise hypercondensation & negate it's downside potential?
;)
Easy
Superheat it;)
^ LOL...
Would this not need to be hypersuperheating?
Hmmm... wondering if I should throw equalizer lines and liquid pumps into the discussion... lol
Hmmm... wondering if I should throw equalizer lines and liquid pumps into the discussion... lol
Would these happen to be of the 'hyper' variety? :eek:
mikeref
20-09-2010, 12:44 AM
Alright, SO, overcondensing is not a physical event that occurs in any refrigeration system right? Or maybe its taken for granted and called by another name because no amount of quantum physics can make it happen on paper. Just as clouds float with tons of water overhead,( workout the dynamics of that),overcondensing is a real event in my opinion, call it what you will, it will always be around.. mike.
mad fridgie
20-09-2010, 01:09 AM
Alright, SO, overcondensing is not a physical event that occurs in any refrigeration system right? Or maybe its taken for granted and called by another name because no amount of quantum physics can make it happen on paper. Just as clouds float with tons of water overhead,( workout the dynamics of that),overcondensing is a real event in my opinion, call it what you will, it will always be around.. mike.
Condensing in refrigeration terms is changing a vapor to a liquid, if all is coverted to liquid then it is condensed, as you cool it the voulme will reduce, then keep cooling it will solidify, 'CONDENSING THE VOLUME" . Incorrect pressure drop is a real event and can be caused by an over sized condensor "thus over condensing" just words, not fact.
I do not think anybody is saying the problems do not occur when the precieved term over condensing is used, just that term its self is incorrect.
mikeref
20-09-2010, 04:52 AM
Sorry for being direct and brutal, but fitting a pressure switch for keeping the condensing pressure high enough to avoid low pressure alarms doesn't involve any of these wasted arguments of yours.
Actually, I think that refrigeration engineers prefer to have themselves payed (read: overpayed) for charging refrigerant than actually spending some time and brain to repair units and fix the problems once and for all.
Then, they come here and whine like sissies about "overcondensing" except that such phenomenon doesn't exist anywhere else than in their huge ignorance.
I was recently working on an old Carrier 50k14 with origional condenser, Thought, this old girl deserves a new condenser with hp stages on 2 of 3 fans BUT NO, owner doesn't agree so it can under condense in summer(with constant breakdowns ref: quote above), or move too much air+ waste energy in the cooler periods:confused:..mike
NoNickName
20-09-2010, 07:36 AM
And why are you asking the owner in the first place? Is he/she a refrigeration engineer or something?
TRASH101
20-09-2010, 01:01 PM
I do not think anybody is saying the problems do not occur when the precieved term over condensing is used, just that term its self is incorrect.
Hello Mad
It would appear that the biggest problem is that people are looking at the term "over condensing" far too subjectively.
Condensing in refrigeration terms is changing a vapor to a liquid, if all is coverted to liquid then it is condensed, as you cool it the voulme will reduce, then keep cooling it will solidify, 'CONDENSING THE VOLUME"
This is not strictly true is it?
Remove heat to reduce the enthalpy therefore increasing the density. i.e. liqiuid doesn't have to be formed to condense! (check the definition if you like)
This is not just my opinion.
The definition of "over" (if we can agree) is in our case a surplus, too much etc...
So if NNN, Mad, Gary can prove that it is impossible to remove "too much heat" at the condenser. Then I will be a convert to the "doesn't exist" state of mind.
NoNickName
20-09-2010, 01:13 PM
First of all, it is impossible to solidify a F-gas refrigerant. There are 3 possible states of matter, but only combination of two of them is possible in case of f.gases: vapour (or gas for supercritical state), vapour + liquid (two-phase equilibrium), liquid.
Exactly as vapour can exist in superheated status, so subcooled liquid can exist.
What is commonly referred here as "overcondensed" is actually "subcooled liquid".
Secondly, I never said that it is impossible to remove too much heat at the condenser (too much compared to what?). I stated that the term "OVERCONDENSING" is as wrong as "OVERKILLING" despite the latter being used in several forensics criminology papers, as the status to which a body is being inflicted multiple deadly wounds, but only one of them is the killing hit.
Let's inject a theoretical element into the discussion:
Q'evap + Q'comp = Q'cond (1st Law of Thermodynamics)
If the condenser heat output increases due to any reason whatsoever, then so must Q'evap+Q'comp. For Q'cond to increase, the HP must lower on the refrigerant vapour bell (just look at the vapour & liquid end-stops for clarification).
In general, the compressor probably doesn't alter too much => Q'comp~const, so Q'evap must increase.
According to the log(p)-h diagram for the vapour compression refrigeration cycle, this would imply that the LP line must lower itself on the vapour bell, as well. Since the TX controls superheat, there is no mechanism to prevent the whole cycle 'slipping downwards' on the log(p)-h plot.
http://i55.tinypic.com/118hcw3.png
TRASH101
20-09-2010, 01:54 PM
NNN
First of all, it is impossible to solidify a F-gas refrigerant.
I never claimed it was possible to solidify f-gas and I refer you to alternate definitions of condensing that are applicable.
Secondly, I never said that it is impossible to remove too much heat at the condenser (too much compared to what?).
I concede that "over" is in itself a subjective term and DesAs' post helps to highlight this (and this in itself state it must exist for everyone to see if everyone can agree on what is too much:D)
I stated that the term "OVERCONDENSING" is as wrong as "OVERKILLING" despite the latter being used in several forensics criminology papers, as the status to which a body is being inflicted multiple deadly wounds is found, but only one of them is the killing hit.
From that I can only see that you are convinced that that condensing is a change of state and not a change in density brought about by a change in enthalpy ( A definition I don't subscribe to)
NoNickName
20-09-2010, 02:30 PM
From that I can only see that you are convinced that that condensing is a change of state and not a change in density
Condensation is the change in the phase of matter from the gaseous phase (of an element/ chemical species) into liquid droplets
http://en.wikipedia.org/wiki/Condensation
It's not me who is convinced... :D
I'm not sure what the argument is about. Even if we can twist the definition enough to make "overcondensing" a real word, it still doesn't describe the problem.
The problem is reduction of liquid flow.
In a stable series loop, the mass flow is equal at all points, so reduced flow at any point is reduced flow at every point.
I'm not sure what the argument is about. Even if we can twist the definition enough to make "overcondensing" a real word, it still doesn't describe the problem.
The problem is reduction of liquid flow.
In a stable series loop, the mass flow is equal at all points, so reduced flow at any point is reduced flow at every point.
To add further to the discussion - how do we know there is reduced mass flow in the system? How is this measured, or observed?
Reduced suction pressure = Reduced mass flow
Hmmm... unless the compressor is inefficient
NoNickName
20-09-2010, 06:00 PM
Reduced suction pressure = Reduced mass flow
Hmmm... unless the compressor is inefficient
Or unless it's inverter driven on suction pressure.
Reduced suction pressure = Reduced mass flow
Hmmm... unless the compressor is inefficient
Take a look at the log(p)-h diagram I sketched. As Q'evap stabilises to re-gain thermodynamic equilibrium, it lowers LP.
Could this be interpreted as the lowering of suction pressure, you are observing? Would this then necessarily imply mass flow reduction?
monkey spanners
20-09-2010, 06:12 PM
So over condensing causes under evaporating......
Jon :p:D
Assuming constant compressor volume and speed, it comes down to density of the vapor being pumped. Higher compressor inlet density (higher LP) means more refrigerant pumped and lower density means less refrigerant pumped.
IOW, on each downstroke of the piston, higher pressure will force more refrigerant into the cylinder and lower pressure will force less refrigerant into the cylinder.
Assuming constant compressor volume and speed, it comes down to density of the vapor being pumped. Higher compressor inlet density (higher LP) means more refrigerant pumped and lower density means less refrigerant pumped.
IOW, on each downstroke of the piston, higher pressure will force more refrigerant into the cylinder and lower pressure will force less refrigerant into the cylinder.
Ok, that makes sense. Interesting.
Beginning to look like a runaway downwards unstable situation for the evap in such a way that the cycle continues to slide downwards. Mmhh... must surely stabilise somewhere in the real world - where?
mad fridgie
20-09-2010, 09:00 PM
Yes you can solidify just about all refrigerants, helium is however a problem, simple example R744, carbon dioxide, soild commonly known as dry ice. (its all about how cold you go)
Increaseing the density, means reducing its volume by mass.
Over condensing if we are going to use the term simply means incorrect pressure differential over the system,
Quality
20-09-2010, 09:05 PM
Yes you can solidify just about all refrigerants,
Its called melting point and yes its that point from liquid to solid or vice versa
Beginning to look like a runaway downwards unstable situation for the evap in such a way that the cycle continues to slide downwards. Mmhh... must surely stabilise somewhere in the real world - where?
The TXV goes wide open, so the flow is governed by the orifice size and current dP, assuming there is solid liquid at its inlet.
It is also possible for the liquid flow to be held back further upstream. Supermarket systems come to mind, where the liquid is held in the condenser because the receiver pressure exceeds condenser pressure.
Segei
20-09-2010, 10:00 PM
Actually, a refrigeration plant is selfbalancing system. Assume that refrigeration load has increased. If compressor volume capacity is constant, suction pressure will increase. At higher suction pressure mass capacity will increase. At certain suction pressure and at certain temperature in cold room this system will be balanced. However, we have a question. Does this new temperature in required rage of temperatures? The same is on the high side. During periods of cool weather, condenser capacity will increase. However, at certain point will be the balance between compressor capacity and condenser capacity. Do we have enough pressure to move liquid in the plant?
lawrence1
20-09-2010, 11:11 PM
Gary,
Throw in a equilizer line between the inlet of the condenser and the receiver and see what happens.
Gary,
Throw in a equilizer line between the inlet of the condenser and the receiver and see what happens.
Yep... that works as long as the condenser is above the receiver. The pressures are equal and gravity moves the liquid.
mikeref
21-09-2010, 12:03 AM
And why are you asking the owner in the first place? Is he/she a refrigeration engineer or something?
No, the owner of the building is the man with the money. I have to have his approval or i don't get paid. Its would suprise you to see the amount of mismatched and struggling refrigeration equipment there is about. Yes it can be fixed but i don't work for free.
mad fridgie
21-09-2010, 02:09 AM
No, the owner of the building is the man with the money. I have to have his approval or i don't get paid. Its would suprise you to see the amount of mismatched and struggling refrigeration equipment there is about. Yes it can be fixed but i don't work for free.
What you do not work for free, what sort of refrigeration engineer are you, very good answer!
mikeref
21-09-2010, 02:32 AM
What you do not work for free, what sort of refrigeration engineer are you, very good answer!
Yeh, not entirely true, how many times have i pulled "clients" out of trouble, put them on 30 days and they don't pay:(:off topic:
NoNickName
21-09-2010, 07:25 AM
You see, you're doing it wrong. You ask your customer about what YOU have to know and what you have to to do to fix it.
He doesn't know, wants to keep costs down, you leave and the unit is still broken.
My way of doing it: fix it and get paid for the good job done. Customer doesn't need to know what I did as long as I did it right. A pressure switch is not an excuse for not paying. You don't even need to mention it in your report (10 gbp cost? Less).
احمد محمود م س
23-09-2010, 07:40 PM
it nice wards
Rallings
24-09-2010, 10:50 AM
I think the term 'over condensing' is a relative term thus relative to the system's condensing requirements.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.