what is the cause of discharge line high pressure? please answer ASAP thank you.

ibraheem
27-08-2010, 11:54 AM
equipment capacity in quetsion, check the design capacity and selected machine

Lexicon
27-08-2010, 12:11 PM
this is a refrigerated fishing vessel using hasegawa refrigeration compressor. The condenser tubes and the coils have no leaks. We have no problem at the start of the operation but after two days the operation discharge pressure goes up.What is the problem? Can you help me?

taz24
27-08-2010, 12:22 PM
this is a refrigerated fishing vessel using hasegawa refrigeration compressor. The condenser tubes and the coils have no leaks. We have no problem at the start of the operation but after two days the operation discharge pressure goes up.What is the problem? Can you help me?


It's not condensing.....

Do you have water flow through the condenser??

taz


.

Lexicon
27-08-2010, 12:36 PM
yes. And the temperature is normal.

NoNickName
27-08-2010, 12:50 PM
You have a clogged condenser. Probably algaes or harbour garbage.

sedgy
27-08-2010, 12:56 PM
hi lexicon, have you cleaned the sea water inline filter? is thje cargo hold doors sealed most of the day? when was the system last serviced? let us know the outcome,

Lexicon
27-08-2010, 01:01 PM
We have opened and checked the condenser tubes and it is clean. But still, the discharge pressure is high. We have also set the cut off pressure switch to be able to continue our operation but the pressure still goes up.

Lexicon
27-08-2010, 01:03 PM
hi lexicon, have you cleaned the sea water inline filter? is thje cargo hold doors sealed most of the day? when was the system last serviced? let us know the outcome,


Yes we have cleaned. But we open the cargo hold doors when we put our catch fish inside the blast freezer. We have serviced the service last month.

NoNickName
27-08-2010, 01:05 PM
The filter is clean, but you may still have algaes vegetation in the condenser tube. Did the blast freezer stand by for a long time unattended?

Lexicon
27-08-2010, 01:15 PM
The boat will go to the port to unload the catch for fifteen days. It will go fishing again after unloading the catch. So the blast freezer is in stand by only for fifteen days. We will open the condenser again tomorrow to double check the tubes if there are still algaes vegetation.

ref717
27-08-2010, 07:48 PM
If your condenser is free and clean, baka may air or non-condensables ka sa system mo Kabayan. Are you using NH^3?,what is your operating suction pressure? or maybe you have restrictions in the condenser water flow or sa high-pressure line from comp. to receiver tank..

Lexicon
28-08-2010, 05:24 AM
No, we are using R22. Thank you very much sa advices mo check ko ulit system namin.