Hi all, I am an Aussie currently living in the UK and over working in facilities maint! :rolleyes:

I am keen as to get back in to my Trade a/c ref. Not sure if im even typing on the right forum cause im brand new to this site.

One of the sites i am currently looking after has two Carrier chillers I am after some info on them.
Model# 30RA-160-A0225-PEE

There is currently an alarm on circuit A alarm is 34 'high pressure switch not reset or cp reverse rotation?' what is cp refering to? I have reset the chiller but the fault returns so am currently running circut B only. If any one could help out that would be great

cheers

serviceman
22-07-2010, 06:02 PM
SUB-MODE KEYPAD
ENTRY ITEM ITEM EXPANSION COMMENT
CRNT AXXX or TXXX CURRENTLY ACTIVE ALARMS ACTIVE ALARMS (AXXX) OR
ALERTS (TXXX) DISPLAYED.

CRNT
RCRN

NO Use to clear active alarms/alerts
NO NO Flashes
YES Select YES
NO Alarms/alerts clear, YES changes to NO

salam
22-07-2010, 07:13 PM
hi bro check condensing pressure &fan status :(

Brian_UK
22-07-2010, 10:56 PM
Do you need any documentation for that unit ?

http://eto.carrier.com/lit.asp

Select the model you have and click on search.

daniel*86
26-07-2010, 01:32 AM
Hey
"CP" refers to compressor. The fault indicates that thers has been no change between the suction and discharge pressures once that compressor has been called for. Possibe causes is a faulty HP,(open circit); No output off board or faulty compressor contactor coil. Let us know how you go.