View Full Version : mitsi comp resistance
refaircon
03-07-2010, 11:18 AM
as title what should be the resistance reading for a comp on the below unit
puhy-250mf-b
martinw58
03-07-2010, 02:46 PM
about 0.72 ohms at 20 oC
refaircon
03-07-2010, 04:58 PM
lad is getting 0.4 across always
Careful when dealing with low resistances: measure a short across the test leads first to zero reference the meter reading, then you can get a more accurate measurement.