Log in

View Full Version : Calculate Operating Expense on Walk In's



thcri
29-06-2010, 03:14 PM
I am trying to some information for a large customer of mine who is doing an evaluation of the expense to pull a walk in cooler back down after they leave the door open for an hour. We know that the temperature is averaging up 4 degrees during this period. How much does it cost to pull back down?

frank
29-06-2010, 05:15 PM
Measure your system running amperage for the time it takes the cabinet to drop the 4 degrees and multiply it by the cost per kWh

Example:

Time taken, say 3 hours
Current draw, say 10Amps
Amps x Voltage (10 x 230 UK) = 2300W or 2.3kW
2.3kW x 3hrs = 6.9kWh
6.9kWh x cost per unit = cost to pull down 4 degrees.

thcri
30-06-2010, 02:15 PM
that sounds too simple LOL I will pass this on.

Thanks