View Full Version : Manitowoc Ice Machine flood back



richbahama
29-06-2010, 09:56 AM
Have an issue with a Manitowoc Ice Machine SDO452A, unit was flooding back to compressor so we changed the TXV, no luck still getting flood back. So we changed the Harvest valve with no luck. Pressures are within factory settings and low side will drop slightly when running. No ice formation on evap. plate during freeze cycle. Takes about an hour to make ice. Any help would be great.

thebigcheese
29-06-2010, 08:31 PM
could be that the ice plate has started to come away from the evaporater.
have seen this before

richbahama
29-06-2010, 10:45 PM
Have checked the ice plate and all is in perfect order, unit is only about 3 years old. Might try another TXV and make sure nothing got trapped inside since it is oriented upside down on this model.

philfridge
30-06-2010, 10:47 PM
Have you weighed in correct amount of refrigerant ? as most likely cause would be overcharged system. Should not take one hour to make ice if charged correctly.