suction 30 psig,room temp -1c.when room temp.0c begin ice foming on suction pipe.no access to check discharge pressur.comp.amp is normal.refrigerent 404a.
thanks
beeran

taz24
15-06-2010, 08:20 AM
suction 30 psig,room temp -1c.when room temp.0c begin ice foming on suction pipe.no access to check discharge pressur.comp.amp is normal.refrigerent 404a.
thanks
beeran


With a suction at 2 bar (30psi) that gives an evap
temp of about -20 degC.

If your suction line did not freeze I would be worried.

A frosty suction line does not mean liquid is present
it just means the pipe is below freezing.

You need to meassure the temp of the suction so
we can work out superheat and you need to give
some air on air off temps across the evap as well.

taz

.

750 Valve
16-06-2010, 07:35 AM
The only thing wrong is that you are running -20SST to achieve -1 room temp

abet_meneses
16-06-2010, 04:05 PM
is ice build up present on the unit cooler,at -1 C room temp ?if so,may be you have an oversize expansion valve or you may have feeding too much,when adjusting txv always check unit cooler superheat.are all fans running?

acb
17-06-2010, 02:24 PM
30 psi is too high for a freezer and not high enogh for a fridge, so its either undercharged or overcharged, my guess is its an overcharged freezer explaining the ice on the suction line, remove gas and recharge.