This unit has been insalled about a week and was running great, but got a call to go and check the unit this eve (outdoor model PUHZ RP10KVA) about the unit not cooling.
Turned the unit on and the fans run outside for about 2 secs then off and repeats this about 5 times.
The outdoor unit is flashing fault code 3 green and 4 red .
I took the 3 wires off compressor and checked windings, 2 are 1.0 ohms and the other is 0.9.
When power is turned on with these wires disconnected thetre is 23.4v between 2 phases DC and the same fault code appears with the wires disconnected.
I have checked compressor wires where they go onto board and all seems fine.
Has anyone had this problem ?
Regards
Chris
Chris2005
14-06-2010, 10:42 AM
Faulty power board
moondawn
14-06-2010, 06:11 PM
hi chris
i recently ran up a mitsi system and had a problem where the compressor was making a noise and failing to start
had error lights cant remember what these were now.
turned out to be a faulty power board.
cheers lee
Chris2005
14-06-2010, 09:55 PM
Hi lee
The compressor on this unit was doing nothing at all, the fans were the only thing that would run.
only the red wire was live to comp the other 2 nothing.
Its the first time this has happend to me normally mitsi are very reliable.
Regards
Chris
moondawn
14-06-2010, 10:23 PM
Hi lee
The compressor on this unit was doing nothing at all, the fans were the only thing that would run.
only the red wire was live to comp the other 2 nothing.
Its the first time this has happend to me normally mitsi are very reliable.
Regards
Chris
i remember that all wires were live on mine, they were fluctuating i think just over a 100 volts i was told by mitsi that its the power board. someone fitted the power board and its all working now.
cheers lee
Chris2005
14-06-2010, 11:24 PM
My new part will be here in the morning thankfully
Which should save a little ear bashing from the customer :)
moondawn
15-06-2010, 05:05 PM
good luck let us know that it was defo the power board
cheers lee
Chris2005
15-06-2010, 08:32 PM
Hi lee
I got the new board this afternnon and replaced it this evening.
I am pleased to say everything is working fine now :),
What part of manchester are you from?
moondawn
15-06-2010, 09:21 PM
hi chris glad to hear it. i am from urmston what about yourself?
just noticed northern ireland :-)
Chris2005
16-06-2010, 10:32 PM
Hi lee
My grandad used to live in flixton beside woodsend circle , I have a lot of family around that area as I was born there myself .
Hows the fridge trade over there at the min?
Regards
Chris
moondawn
16-06-2010, 11:23 PM
hi chris yeah know it well lived here all my life.
its picking up at the company i work for, got quite a lot of work on so its very busy at the moment mate