View Full Version : Rd-ii sr
freegass
10-06-2010, 08:55 AM
Hello
I'm new user. I need urgently service manual for the unit RD-II SR. I have a problem in the engine diesel overheating. Condenser and radiator were thoroughly cleaned, but the problem persists. Overheating occurs during the cooling cycle. I suspect that the throttle valve X426 compressor or expansion valve is working not properly. The filter-dryer is a new, R404a refrigerant content 3.6kg.
I should be grateful for any help or instructions.
greetings to all
radekklimat
10-06-2010, 09:35 PM
Jak masz problem ze swoim RD to chetnie ci pomoge
500 236 866
What is your regulated suction Pressure, and Head Pressure?
I'm assuming you have already checked Coolant flow, Eng t-stat, Cond fan blade pitch, and position in the shroud, coolant/water mixture, belt tension, and engine Rpm's in low and High speed..
abbsnowman
11-06-2010, 06:02 AM
Manual is too large to email.
The Fox
13-06-2010, 02:17 PM
i know you have said the cooling system is clean, there is a small pipe that connects fron the top of the expanion tank to the top of the rad.the pipe is very small bore ,if the pipe or the fittings become blocked it will overheat and it is quite common for that to happen and is easy to miss.
shaun220
13-06-2010, 07:26 PM
Remove the engine stat, and check. then try the water pump....
gravy258
14-06-2010, 04:36 AM
If everything else is working freely.
usually suction pressure too high.
Put a gauge in the side of the throttling valve, should be 18psi. All the time.
These Yanmar engines only have enough power to do the job, over and above they'll overheat.
freegass
16-06-2010, 07:38 PM
OK. Thank you for your suggestions. I checked all today. Well, the throttle valve is working correctly, 1.2 -1.3 bar in the heating cycle. Question: when the mP should open Thermax valve ?
freegass
16-06-2010, 07:42 PM
Jak masz problem ze swoim RD to chetnie ci pomoge
500 236 866
Na pewno się odezwę.
you will need to fit a guage manifold and tell us what the suction and discharge pressure this is running at . If the discharge pressure is under 200 psi , then i doubt there is an issue with the refrigeration and it will be with the engine . Are you sure the engine temp guage is accurate , does it get so hot it cuts out on alarm?
brm
OK. Thank you for your suggestions. I checked all today. Well, the throttle valve is working correctly, 1.2 -1.3 bar in the heating cycle. Question: when the mP should open Thermax valve ?
At start up and in the beginning of the Heat cycle. Thermax should not cause over heating. it is just a high side pump down valve.
The condenser fan position in the shroud is also very important. Their needs to be at least 3 or 4 cm of fan past the outside lip of the shroud. otherwise the temp on the engine will slowly rise.
Vacoel76
25-06-2010, 06:50 PM
try a check water pump, possibly also on the engine cylinder head was cracked ..