hi all i am having some troubble finding the fault on A unit, when you turn it on the outdoor condenser fan starts and the compressor runs noisily drawing 5 to 10 amps but the indoor unit stays with the lover open and both operation and power lights on but the indoor fan doesnt run, while the outdoor seems to ramp up and down stopping and starting. unit is an inverter 410a, model:
indoor msz-gb50va
outdoor muz-gb50va

unit doesnt fault out as such so it doesnt bring up the flashing fault on the indoor, will this problem be caused by one of the pc boards?

Any help would be muchly appreciated

cheers
Dan

Gingerair
10-06-2010, 09:05 AM
Hi Dan

Does the indoor fan turn easily by hand ? If yes, then check that your indoor unit runs in fan only mode..
Have you got a manual for this unit ?

SpaceManDan
10-06-2010, 09:46 AM
Nah no manual had a bit of a look online but had no love, yes unit runs on fan only fine.

Gingerair
10-06-2010, 10:15 AM
Check your Hotmail inbox..

kkboy
19-06-2010, 08:03 AM
mitsubishi electric a/c dont breakdown. If it was a daikin i could understand your troubles.

Peter_1
20-06-2010, 10:14 AM
You don't have a fault code on the outdoor unit?