View Full Version : walk in freezer compressor



phxjersey
16-05-2010, 04:55 PM
I have a walkin freezer and when the compressor goes into defrost, it doesn't turn back on automatically when defrost cycle in finished.
we are having to push a button to restart it. This ssems to only happen when it is warm outside, being in phoenix this is approx 6 months a year, and had no problem during the winter

NH3LVR
16-05-2010, 05:06 PM
Which button do you have to press to restart it? Describe the unit.

phxjersey
16-05-2010, 05:13 PM
it is a Russell 4 ton compressor,,up top near the fan, there is a small rectangle box with a button to restart, after the defrost cylce has ended, approx 30 min,, or so,,,we find out that after about 1 hour compressor hasnt restarted or kicked back, then we are having to climb on ladder and push button, then the fan and compressor goes back on,,,

coolhibby1875
16-05-2010, 08:01 PM
your condenser will be needing cleaned

ZeroTolerance
16-05-2010, 10:08 PM
I'm not familiar with a reset button but rather a faulty contactor. Sounds like your pulling to many amps which is tripping the reset when the compressor tries to kick back on.

ZeroTolerance
16-05-2010, 10:09 PM
Check your pressures in the system. Maybe high head pressure do to the outside heat?

FEISTY
17-05-2010, 01:16 AM
Check your defrost timer for cycle time and try to be there the next time it goes into defrost. Then test what circuit is open or tripped and follow back to find the cause. Have gauges on system to see if high pressure ramps enough to trip safety. Also connect clamp-on amp probe to check start-up demand. Finally...don't do any service before you test it. Use it as a learning experience. If you fix what you don't know is the problem, you will never know what happened. That way you have a jump on the next call. Good luck.

dirk
17-05-2010, 03:39 AM
As a rule you should know what fault you are rectifying before you press any reset device.