I recieved a couple of weeks ago a service bulletin which no doubt some of you will have seen. It relates to the positioning of a TEV and say's that they can maulfunction if not vertical. Now as far as i am aware TEV's are operated using pressure against an internal spring so what difference does it's location make. Here is the Bullentin apart from the manufacturer blanked out.
Problem:-
######## is now aware that a small number of these units were manufactured with the TEV Valve in a horizontal attitude. This may result in the vale operating in a partially closed manner. This will cause the evap and the TEV to become iced up.
Solution:-
The TEV needs to be orientated so the head is above the body, and the valve should be made as vertical as possible.
Any Comments
Regards
Fatboy
I recieved a couple of weeks ago a service bulletin which no doubt some of you will have seen. It relates to the positioning of a TEV and say's that they can maulfunction if not vertical. Now as far as i am aware TEV's are operated using pressure against an internal spring so what difference does it's location make. Here is the Bullentin apart from the manufacturer blanked out.
Problem:-
######## is now aware that a small number of these units were manufactured with the TEV Valve in a horizontal attitude. This may result in the vale operating in a partially closed manner. This will cause the evap and the TEV to become iced up.
Solution:-
The TEV needs to be orientated so the head is above the body, and the valve should be made as vertical as possible.
Any Comments
Regards
Fatboy