What difference / setback / plus point - will it make if we install the condensers / cooling towers at the same level as that of compressors instead of putting them up at 3500 mm level.
My problem is that the contractor wants it to be 3500 mm above ground whereas I would like it to be at ground level main reason being high construction costs for a 50 Ft x 20 Ft. platform.
I will appreciate suggestions that can be helpful to place the condensers / cooling towers at ground level.
The contractor has the following comments:
1- After condensation liquid flows from condenser always by gravity with certain slope to avoid the liquid trapping in lines .
2- Condenser should always in open Air for optimized condensation process (ITS IN THE OPEN AIR ALREADY)
3- There should always be a certain pressure in liquid receiver at out let of condenser to avoid the vaporization in liquid receiver .
4- From Process design point of view Grasso strongly recommends that condenser should always be placed at certain height
My problem is that the contractor wants it to be 3500 mm above ground whereas I would like it to be at ground level main reason being high construction costs for a 50 Ft x 20 Ft. platform.
I will appreciate suggestions that can be helpful to place the condensers / cooling towers at ground level.
The contractor has the following comments:
1- After condensation liquid flows from condenser always by gravity with certain slope to avoid the liquid trapping in lines .
2- Condenser should always in open Air for optimized condensation process (ITS IN THE OPEN AIR ALREADY)
3- There should always be a certain pressure in liquid receiver at out let of condenser to avoid the vaporization in liquid receiver .
4- From Process design point of view Grasso strongly recommends that condenser should always be placed at certain height