I have an Austral KM20S1D-1 dairy cabinet that's Icing up the first second thirds of the evap coil but not the centre. All fans are working gas level is OK.?????

cadwaladr
04-04-2010, 12:26 AM
t/stat prob or defrost ,diff too close,interval too long,dont forget to clean condensor.

lawrence1
04-04-2010, 01:33 AM
Does it have one evaporator or 2/3 smaller ones?
lj

750 Valve
04-04-2010, 03:40 AM
I have an Austral KM20S1D-1 dairy cabinet that's Icing up the first second thirds of the evap coil but not the centre. All fans are working gas level is OK.?????

what SST are you running? and defrosts?

The XM and KM series cases are pretty good and have never really heard of anything like this happening if they are within manufacturers specs, being KM (which are the metric cases) it will have 1 coil

Pat Milliken
04-04-2010, 04:41 AM
one evap only

Pat Milliken
04-04-2010, 04:43 AM
-6 celcius, defrost 3hr for 15 mins

750 Valve
04-04-2010, 05:54 AM
So 8 defrosts per day @ 15mins, thats as per Austral specs, the -6 is a little low in SST, they are designed for a -3.5 SST at the case (provided you can maintain a constant SST- eg rack system or unloaders on a single system). Running lower can increase the frost load on the case and drop off the airflow, how is the humidity in the shop? Running a lower SST I reckon with 60% and above RH you'd be frosting the coils quickly and losing airflow which it seems you are picking up on the LH and RH ends first.

Pat Milliken
04-04-2010, 10:30 AM
Just been to site again and found that one of the AC systems is faulting. Waiting for the AC tech to repair (wty), will advise outcome

cadwaladr
04-04-2010, 10:41 AM
ah,for every action there is a reaction

lowcool
04-04-2010, 11:58 PM
gday pat
might pay to check superheat setting of your coil also