Log in

View Full Version : trane rtac 250 oil filter replacment



anish
23-02-2010, 05:48 AM
hi guys
As i am working on trane rtac 250 aircooled chiller to replace compressor internal oil filter. please guide me to complete this job. if i could get any service manual it would be very help ful.

:)
anish

HvacKevin
24-02-2010, 01:27 AM
What is the Model #??

HvacKevin
24-02-2010, 02:21 AM
hi guys
As i am working on trane rtac 250 aircooled chiller to replace compressor internal oil filter. please guide me to complete this job. if i could get any service manual it would be very help ful.

:)
anish

Oil filter replacment shouldn't be done as regular maintenance, only if oil analysis shows contamination.

I would start by isolating the compressor and evacuating,then remove oilfilter cover plate.

I would not attemp this repair without the proper procedure from the service manual. Im sure if you contact trane they will help you out with that.

moideen
24-02-2010, 06:15 AM
hi guys
As i am working on trane rtac 250 aircooled chiller to replace compressor internal oil filter. please guide me to complete this job. if i could get any service manual it would be very help ful.

:)
anish
hi anish welcome to re.give me your id(by pvt msg).i can send you the i.o.m of rtac chiller.

Moideen-dubai;)

choochoo!
24-02-2010, 07:47 AM
If you are replacing the oil filter its best to replace the oil reg valve which is located behind the oil filter, as this can be the cause of most oil faults. the filter very rearley needs to be replaced.once you have recovered the gas from the compressor remove the 1/4inch grub screw to relief a small amount of pressure before removing the oil filter access plate. the grub screw is on the front of the oil filter plate.

anish
03-03-2010, 07:19 AM
hai guys
reason to change the filter was this chiller rtac 250 was tripping due to alarm low oil flow immediately after the start and intermediate oil pressure is also going below 70 psi .

choochoo!
07-03-2010, 09:46 PM
it is more than likely to be the oil regulating valve situated behind the oil filter which is causing oil diff trips,
replace reg valve to clear fault

expansion
17-11-2010, 02:06 PM
did you check the oil return solenoid valve and strainer located under the compressor?

goshen
18-11-2010, 04:56 AM
did you check the oil return solenoid valve and strainer located under the compressor?
Hi
and welcome aboard!!!
you should make it a habbit to look at posting date!!!
i think he fixed his problem by now !!!!!:)

anish
27-01-2011, 09:32 AM
hi guys
i have fixed the problem and unit is working ok.
but i got new issue the 1/4inch grub screw to relief pressure in oil filter access plate is having a leak please help

CV_Geardrive
27-01-2011, 11:57 AM
Hi Anish,
Use Trane part number RNG01697.
Regards,
CV

anish
28-01-2011, 06:06 AM
hi
this part number RNG01697 for WHAT?????????

CV_Geardrive
28-01-2011, 06:30 AM
Hi Anish,
This part number is the O’ring fitted in ¼” screw.
Please check with your local TRANE office.
Regards,
CV

anish
29-01-2011, 02:14 PM
Hi
thanks a lot for ur valuable sugestion.