Friend had a question, working on a home built liquid chiller using a TXV.

Has an external equalizer, but seems to not be equalizing enough after shut down to allow a reboot with plenty of time.

Any thoughts?

mad fridgie
12-01-2010, 02:39 AM
I presume you mean "external equaliser" is on TXV, if so, not there to equalise the system, Add anti-cycle timer or change starting method (i bet you are using a PSC start) or add a unload solenoid valve (between suction and discharge)

NoL
12-01-2010, 03:26 AM
Ah yes my bad, does a system like this actually require a solenoid to unload?

mad fridgie
12-01-2010, 03:46 AM
Ah yes my bad, does a system like this actually require a solenoid to unload?
No not really, we need more info

NoL
12-01-2010, 04:03 AM
What info would help?


1hp LG Rotary
2.3kw Condenser coil with fan
30 plate HX
Danfoss TES2 with 01 Orifice
R404a

mad fridgie
12-01-2010, 04:29 AM
What info would help?


1hp LG Rotary
2.3kw Condenser coil with fan
30 plate HX
Danfoss TES2 with 01 Orifice
R404a
Do not know exact machine single phase?, but, is it a Permanent Split Capacitor Compressor (PSC)?, these have little starting torque, change for a relay and start capacitor. or unloading valve, or larger anti cycle time.

NoL
12-01-2010, 05:37 AM
PSC, so yeah just a run cap.
And single phase.
But shouldnt the system be equalizing completely when its off?

Brian_UK
12-01-2010, 07:42 AM
PSC, so yeah just a run cap.
And single phase.
But shouldnt the system be equalizing completely when its off?
Depends on the type of TXV fitted.

NoL
12-01-2010, 06:08 PM
Is there any way to tell which kind of TXV allows this and which don't? I've never seen this, but I normally only work on systems with EEV and captubes.