hi,

does anybody have a suggestion how to utilize ***** (R-410a) from a recovery cylinder that got some water inside it?

how to check for water in a ***** cylinder?

actually, i have plate HX evaporator that leaked and water and refrigerant got mixed. i tried to recover the gas that was inside the system (my mistake) but stopped as soon as i realized it was a bad idea and now i have a contaminated cylinder (not sure).

cadwaladr
06-01-2010, 10:10 PM
send it for recycling

MIST HVAC RA
07-01-2010, 01:11 PM
it means that the cylinder is gone. can't be used?

any way to fix it?

goshen
11-01-2010, 05:33 PM
Hi there vaccum your cylinder down to 200 micron this should clear out the water but first empty it out completly dont try to vaccum a liter of water!!!

Magoo
12-01-2010, 01:50 AM
Multi-vacuum system and break each cycle with oxygen free and moisture free nitrogen, could take a long time, as in 6 > 10 cycles. Time is of the essence. A long time repair.
The test is monitoring vacuum changes with system isolated and no vac pump operating. There is a glide slope graph to interprute leaks versus moisture over extended periods. I cannot find it so cannot forward. Re-cycle old refrigerant and start with new refrigerant.
Hopefully you have sorted the problem initially of water in system, otherwise you will go round in circles.
magoo

Fri3Oil System
13-04-2010, 12:06 PM
Why dont you just clean the cylinder and reuse that 410A recycled?

There is a method to clean any RAC circuit from water, and a cylinder is kind of a small circuit, just one syphon to clean, very simple.

sedgy
13-04-2010, 12:53 PM
reclaim the vapour into new reclaim bottle through large dryer gas gone , tip up bottle pour out water heat up bottle 100c vacpump, change oil in vac pump , job done,

goshen
13-04-2010, 05:44 PM
i think after 3 months all the water evaporated!!!

sedgy
13-04-2010, 06:29 PM
how can water evaporate in a pressurised bottle mixed with refrigerant?

goshen
13-04-2010, 07:24 PM
Hi sedgY i dont think u got my point ,this thread is 3 months old !!!!!!

Peter_1
25-02-2011, 10:46 AM
Goshen, Sedgy's advice was for me the only advice that responded correctly to the original question, no matter if it's 3 months old. Threads in RE are very often consulted for later advise by other members, searching for technical info.

sedgy
25-02-2011, 05:47 PM
peter 0ne, thank you for your kind words = so wheres the rep point then ?

Peter_1
25-02-2011, 05:57 PM
You're right, sorted out yet

sedgy
26-02-2011, 12:13 AM
peter one, thank you for your kind gesture, but I am sure we will agree to have our own ideas?
and you youngsters will have to put up with us old ones sticking up for what we have allways stood for, fair play and a fair hearing ? thank you.
yours sedgy,

sedgy
19-03-2011, 09:44 PM
hi all just testing, thought it was locked?