03-12-2009, 09:25 AM
Hay everyone,
I have this problem with a Freezer unit.
In normal operation the the unit will cut in at -18C and cut out at -20C.
Here is my problem when the temp is -20C and the unit is supposed to be cutout until the temp is -18C but it short cycles a few time until the temp is -18C then a solenoid opens and the compressor starts pulling the room back down to -20C
I noticed that the solenoid on the outlet side was just frosty and when touched the inlet and outlet of the solenoid the inlet was warm and the outlet was cold.
Could this mean that the seat in the solenoid is not seated properly as there is some refrigerant bypassing which is causing the unit to short cycle during the period it is supposed to be off.
thanks