PDA

View Full Version : proplem62



renos tsiartas
18-11-2009, 10:17 PM
I chiler model 30gx 122 and has a proplem 62.
is good to know how i will change the oil level swcith with out recaver the R134(54kg).
Do you think has other proplem?

Brian_UK
18-11-2009, 11:10 PM
Do you have a problem with the oil pressure sensors?

Alarm 62 seems more concerned with the oil flow, filter etc.

serviceman
20-11-2009, 02:14 PM
changing the external filter oil and verifies the differential pressure of domestic oil filter
Best regards

renos tsiartas
20-11-2009, 04:52 PM
thaks you for the information .Do you the same model chiller from carrier

Gibbo
20-11-2009, 07:33 PM
You would need to recover all of the refrigerant and oil to change the oil level switch. However your problem is the oil pressure differential. Change external and internal oil filters and that should clear your problem. No need to recover the refrigerant for this problem

renos tsiartas
23-11-2009, 08:30 PM
thank you for the information.i cant find the internal oil filter.where s it?

Brian_UK
23-11-2009, 11:01 PM
thank you for the information.i cant find the internal oil filter.where s it?
r.t.f.m. .