Hi, just looking for some info as to why we have Centrif Chillers on high voltages like 3300 and 6600 volts ?

NH3LVR
23-08-2009, 09:21 PM
Centrifugal chillers are not my thing, but I would assume it is because of the Horsepower. Lighter wiring and smaller contacters as compared to lower voltages.

Toosh
24-08-2009, 11:22 AM
Hi, one thing springs to mind lower amperage, I may be wrong.

goshen
24-08-2009, 05:41 PM
Hi, one thing springs to mind lower amperage, I may be wrong.
hi ther u are 100% correct the higher the voltage the lower the ampreage!!!:D

Toosh
25-08-2009, 01:46 AM
hi ther u are 100% correct the higher the voltage the lower the ampreage!!!:D

Hi Goshen I used to look after 25 carrier 17/19FA centrifugal chillers 600TR if I recollect the full load amps were 198, in Saudi Arabia for ARAMCO they were used as district for the Company town.

Norm

Yuri B.
25-08-2009, 07:28 AM
Hi, just looking for some info as to why we have Centrif Chillers on high voltages like 3300 and 6600 volts ?

This comes to mind first. Motors with high output powers are fed by high voltages - less currents, as said above - less power losses; they are smaller - less material (iron and copper) used for their construction.