View Full Version : Mitsubishi vrf inverter board dip switchs



Paultighe
09-08-2009, 03:33 PM
Hey folks, anyone know what the dip switches on just the compressor inverter board 1 to 4 are used for, possibly self test ? ?

Lowrider
09-08-2009, 04:55 PM
If you send me a pm with you e mail address I can send you the service handbook, should be in there!

Paultighe
09-08-2009, 05:07 PM
Cheers. thermal@*****.net (thermal@eircom.net)

Lowrider
09-08-2009, 06:46 PM
Message send! Please edit the mail and make your e-mail address unreadeble to prevent spam!

Thermatech
09-08-2009, 09:52 PM
If you want to test the inverter output without the compressor connected to ensure the inverter has correct output
then
you need to put SW1-1 to ON possition.
This will stop the inverter reporting low amps fault & allow you to take readings.
but
its a bit like the test run function it counts down a time period & then switches unit off to prevent the unit being left permanantly in this test condition.

Paultighe
10-08-2009, 07:11 PM
Cheers handy, the very first vrf units would run the inverter with the compressor tails disconnected.