Hello;
I want to charge 4 coldrooms:
1-positive temperature R12
2-negative temperature R 12
3-positive temperature R 502
4-negative temperature R502
What is the suction (low gauge)pressure for each case
Note that we do not know the refrigerant amount

Brian_UK
26-07-2009, 11:22 PM
We have no idea until the system is running and at design temperature.

Magoo
27-07-2009, 02:38 AM
Why are you using R12 and R502, have you not heard of global warming, living a desert area of the planet.

lowcool
27-07-2009, 06:48 AM
just proves there is a long way to go with this issue.

Brendon86
07-08-2009, 03:08 PM
Sounds like you need an experienced technician to help you. There is no way to answer your question correctly. Another tip when charging a system is knowing what to saturated suction temperature to expect before you charge your system. It all depends on the conditions on the day and how the systems are designed. Try to work in temperature to. A pressure is just a pressure and means nothing unless you have a PT chart.

coolstuf
07-08-2009, 09:51 PM
Brendan is right, a pressure is just a pressure, use temp. By the way, you can definitely not charge any system by pressure:(