View Full Version : need help for Tecumseh compressor



frankfrank
14-07-2009, 08:32 AM
carrier Model: 48TJD006-501YA. 208/230V 3PH
Tecumseh Compressor Model: AVB5558EXT.200/220V 3PH
one year new
When I turn the A/C on, the compressor soundss very noise, and the suction line pressure is: 50psi. and high side pressure is: around 400psi. condenser air inlet and outlet is normal. and inside supply air is not cold enough. Can any technician tell me what is the problem? is something wrong with the compressor or somewhere stuck (block) in the high side? thank you very much

Brian_UK
14-07-2009, 09:02 PM
And... the refrigerant is ??

Gary
14-07-2009, 09:12 PM
condenser air inlet and outlet is normal

"normal" is an opinion, not a temperature measurement.

Peter_1
14-07-2009, 09:15 PM
Right on the spot Gary.
I think you should check first the fertibilisation.

philfridge
14-07-2009, 10:56 PM
You should need to blow out condenser coil and report back with results.

crit71
22-07-2009, 11:29 PM
If the temperatures are indeed "normal" then it may be that you have none condesibles in your condenser reducing the capacity of it.
Either way...it sounds like you need a fridge dude.

cuteboy696
26-07-2009, 09:44 PM
you replace your cappliry tube or expension valve

cuteboy696
26-07-2009, 09:46 PM
you check your filterdrier is to warm or normal if its to warm your condenser is durty you clean and wash your condenser

Magoo
27-07-2009, 02:44 AM
To repeat Brian UK's question...., the refrigerant is .. ? You have hundreds of possible options these days, just pick one.

paddyaircon
05-08-2009, 07:21 PM
sounds like non condensibles in there, or perhaps a blocked condensor- slow or reverse direction condensor fan?