Need some help please, I went to upright commerical freezer, needed re-gas, did not have time switched off, went back in 2 weeks, replaced dryer checked for any blockages as capillary, re-gased but when switched on, compressor (Embraco NJ2212GK R404) just getting hotter and hotter, checked capacitors ok, any idea's guys what this could be much appreciated thanks.

Clk320_Greg
09-07-2009, 11:51 PM
Need some help please, I went to upright commerical freezer, needed re-gas, did not have time switched off, went back in 2 weeks, replaced dryer checked for any blockages as capillary, re-gased but when switched on, compressor (Embraco NJ2212GK R404) just getting hotter and hotter, checked capacitors ok, any idea's guys what this could be much appreciated thanks.

What was the inital fault? how did you diagnose re-gas? where had the leak occured? did you fix the leak?

fridge 09
10-07-2009, 09:53 AM
Yes i fixed the leak it was the service valve, So i fitted new one thanks

123-steve909
10-07-2009, 01:07 PM
Need some help please, I went to upright commerical freezer, needed re-gas, did not have time switched off, went back in 2 weeks, replaced dryer checked for any blockages as capillary, re-gased but when switched on, compressor (Embraco NJ2212GK R404) just getting hotter and hotter, checked capacitors ok, any idea's guys what this could be much appreciated thanks.


wrong compressor for a start, the embraco is a 34cc 1 1/2hp compressor. even on there 2 door freezer (garnet/sapphire/jade/zircon) the biggest they used is a Lunite 26cc.

cheers
steve

tonyelian
10-07-2009, 09:07 PM
hi fridge9
u have started wrong way u changed drier before u check the compressor or any thing else.
u have to prvide more info so u can have more help.
check the motor winding& amp draw.
and abour the service valve i thik some body else has came before u to this job

fridge 09
14-07-2009, 12:10 AM
Hi guys, I have changed the dryer, i have blown nitrogen around the sysem and through the capillary all clear, then put gas in R404 the compressor did not start it was just getting hotter and hotter, Checked windings all ok, i hope this helps thanks

fridge 09
14-07-2009, 12:37 AM
You're right about the compressor i just checked its a 34cc 1HP, much to big, as its only a single door, a 20cc would be big enough for that freezer, may be it is to big and its burnet itself out!

Andy W
14-07-2009, 07:16 AM
If the compressor did not start but just got hotter and hotter then it is seized (locked rotor), it must be going out on the klixon then.

fridge 09
14-07-2009, 10:55 AM
Yes it was going out on the klixion, then after a while it was re-setting its self, what size compressor would you recomend for a 600Ltr single door freezer then, thanks for you're help.

123-steve909
14-07-2009, 01:23 PM
Yes it was going out on the klixion, then after a while it was re-setting its self, what size compressor would you recomend for a 600Ltr single door freezer then, thanks for you're help.


600L!!!!!!!!!! i was thinking a 26cc compressor for a 2 door!

one door compressor would be around 15 -18cc. the correct compressor for this cabinet is a lunite CAJ2428Z (15.2CC)

fridge 09
14-07-2009, 09:47 PM
Thanks Steve, for your advice, will have a look