I'm after parameter list and program instructions for a pool heat pump Zodiac Eden Pac 6.

I want to change time limits between defrosts.

Can any one help?

Brian_UK
29-06-2009, 11:57 PM
Can only find the owners manual which says that defrost is dependent on coil temps and the defrost time is based on compressor run time.

Not sure how you would change those.

danielt_smith
30-06-2009, 04:33 AM
Found owners manual on the internet. There was a reference to regulator parameters on the EURO∞FK digital regulator??? Is there a installers manual with such parameters. Supplier in Australia is unable to help.

Unit was out on a low refrigerant alarm. The client complained of ice build up on the bottom of the coil. Unit was able to cycle through defrost and correct refrigerant charge was confirmed. Fans, coil, and unit placement is all correct. The next logical answer was to decrease min. time between defrost cycles.