View Full Version : Daikin Leak
Crypton
27-06-2009, 09:46 PM
Found a leak on Friday on A Daikin 3 pipe outdoor. Model number of the unit is a REYQ8m7w1B. What is the procedure to make sure all the valves are open when reclaiming the remainder of the gas so I get all the gas out?
Clk320_Greg
27-06-2009, 11:02 PM
Leak on the condensor on just on the system?
Crypton
27-06-2009, 11:20 PM
Leak on the condensor. One of the small pipes inside the unit.
SkyWalker
27-06-2009, 11:58 PM
i think you can do a master reset which will drive all the valves open, i know it works on all bs box and fan coils but not sure about condensing unit, i cant remember exactly how but its done via the push switch buttons on o/d main pcb
Crypton
29-06-2009, 09:46 PM
Thanks for the help hopefully I will find something.
puddleboy3
30-06-2009, 12:32 AM
You need to set mode 2 setting 21 on the outdoor PCB, this will open SV's and expansion valves to allow correct vac, pressure test etc. Dont suppose the leak was at a small capillary line just off the oil seperator?
Crypton
04-07-2009, 04:06 PM
Thanks for the info. I was not aware of the setting but I managed to reclaim all of the gas. It was a fluke finding the leak the lad that I was with spotted a small trace of oil on a pipe sprayed some bubbles on it and there she was.The leak was on a small 3/8 pipe on the liquid side.