05-06-2009, 03:13 AM
when sizing up a hot gas defrost differential valve installed in the discharge line what is all the information that is required?
-Rack horsepower?
-Discharge line size?
these would be my guesses...
anyone know for sure whats needed? thanks.
Magoo
05-06-2009, 04:34 AM
Minimal pressure increase when not hot gasing, so you don't artifically increase discharge pressure at compressor, ie restrict flow rate.
magoo
joe magee
06-06-2009, 02:21 AM
That's correct. The engineering department ask for compressor models and discharge line size.:)
Peter_1
06-06-2009, 12:53 PM
I should say max capacity flowing through it and allowable pressure drop.