View Full Version : scroll compressor failure



sagar45
14-05-2009, 03:08 PM
i facing a problem that the copeland scroll compressor dont building a pressure .

The pressure are 160 PSIG at suction and discharge both end is same .
Also compressor is taking 10 A current.

sagar45
14-05-2009, 03:09 PM
can anyone suggest me what are checkpoint to diagnoss the problem.

Sridhar1312
14-05-2009, 04:24 PM
If suction and discharge are high then it is overcharged.
Please remove refrigerant and ensure the suction is around 65 /70 psig and discharge is 240 psi if the ambient is 35 for R-22.
please measure the subcooling and superheat so that clear picture can emerge

Yuri B.
14-05-2009, 05:35 PM
Check phase sequence.

Yuri B.
14-05-2009, 05:37 PM
I mean your scroll may be turning in the wrong direction.

sagar45
15-05-2009, 06:52 AM
first we find that the compressor is taking 80A current
Then we check the terminals at compressor end we found loaas terminal .
Then we started the system we found the leakage .
By brazing and vaccuming the system we charged the refrigerant from suction side we found the pressure is not builting . For that purpose we check the current the current is 10A i.e. normal.

I think that there sholud bre failure of Scroll hence the motor is running bt not biluding the pressure.

Can Anyone suggest on this?

Yuri B.
15-05-2009, 07:49 AM
Probably, first your system started loosing refrigerant, the reduced amount of gas did not cool the comp, the latter heated, thermically expanded and jammed. The loose contacts are, probably, the result of the monstrous current of the jammed motor. When the comp cooled down and the jam went it run, but, on my view your compressor now needs opening and repair.

Yuri B.
15-05-2009, 07:57 AM
The current and compressor's thermal protection need be improved, I wonder how motor's windings survived.

ateeq.baig
15-05-2009, 09:16 AM
dear
there is only two posibilities
one is the compressor which you are using is auto stop modle in this model the comp has a internal safty when comp will heat up due to high or low votage or any other reason the comp will stop its pumping and you have to switch it off for three or four hours
Second is this you have to check you phase sequence it should be clock wise
Note
if the suction pressure will too low then the comp will react same like that

nike123
15-05-2009, 07:30 PM
Is that unit heat pump with 4-way valve?

sagar45
21-05-2009, 12:50 PM
Our scroll compressor is opening on ASTP .

What are the resaons can anyone suggest .

nike123
21-05-2009, 01:07 PM
ASTP is Apollo-Soyuz Test Project?:confused:

sagar45
21-05-2009, 01:37 PM
As we know the ASTP opens at Critical Temp i.e. 135 Deg C.
The reasons will be loss of refrigerant , gas quantity low. But in this case gas quantity is ok . also there is no refrigerant leak.
Also condenser and air flow is OK .

The compressor is ZR94 having Capacity 23.3 KW
and POwer consumption is 6.75 KW .

Is condenser is Short?
Thats Why The discharge temperature is overshooting.

sagar45
21-05-2009, 01:37 PM
Please give your comments

nike123
21-05-2009, 02:11 PM
Is that unit heat pump with 4-way valve?


Please give your comments


We can not comment further if you don't answer at asked questions!

Is that unit heat pump with 4-way valve?

D.D.KORANNE
22-05-2009, 04:50 AM
Compressor is not probably pumping ; current drawn mentioned could be the magnetising current.

raviperumal
27-05-2009, 08:17 AM
Hi,

To confirm the compressor pumping effect through the following ways:

Method 1: By expansion valve

Step 1; Take out the expansion valve bulb from evaporator outlet and immersed into a cold water (probably 20 Deg C less than ambient)
Step 2: Check the suction pressure reduction is happening drastically / not
Step 3: If suction pressure reducing drastically than compressor pumping is ok. If not compressor pumping is failed.

I hope this will help you to resolve the issue.

Regards,
Ravi perumal

senthil_idmc06
04-06-2009, 05:00 AM
Dear All,
It's a well equipped PLC based vapour compression system. We are using grasso screw compressor. One of the compressor is getting trip often, That time it's control panel gets the "alarm 37 " .I went through the manual and observed that there is some loose connection or defective module.

I rectified the above factors. Then also it's getting trip some times.

can any one suggest some other possible causes.

Regards
Senthil

DRAISLAND7
06-06-2009, 02:31 AM
If both suction and discharge are the same then the valves are bad, the amp draw should be 75% of the RLA on the M# tag

Magoo
06-06-2009, 02:58 AM
Sounds like the scroll is screwed.
Hey Nike. I did enyoy, LMAO, your reference "Apollo Soyus Test Project" what ever connection.
The first time I have seen a Croatian sense of humour.
magoo

icecube51
06-06-2009, 07:58 AM
Hey Magoo,

you aint seen nothing yet dan. don't leave the gate open for Nike he become's unstoppeble. (LOL)

Ice

nike123
06-06-2009, 05:58 PM
D
can any one suggest some other possible causes.

Regards
Senthil

I suggest that you start your own thread, and not stealing someone other thread.:rolleyes:

brunstar
06-06-2009, 06:16 PM
either reverse phase if it is noisy, or the scroll is damaged.
if it is a new comprressor you will have your phases reversed or the 4 way valve is jammed in between and you are pumping your discharge into your suction.

nike123
06-06-2009, 06:26 PM
Hey Magoo,

you aint seen nothing yet dan. don't leave the gate open for Nike he become's unstoppeble. (LOL)

Ice
Ice???:eek::eek:

:D:D:D

nike123
06-06-2009, 06:28 PM
We can not comment further if you don't answer at asked questions!

Is that unit heat pump with 4-way valve?


or the 4 way valve is jammed in between and you are pumping your discharge into your suction.

........................;)

nike123
06-06-2009, 06:33 PM
The first time I have seen a Croatian sense of humour.
magoo

It is not that original.;)
Someone say ASTP and you go like this:

http://tinyurl.com/p7m6yv

And third result is:

http://en.wikipedia.org/wiki/Apollo-Soyuz_Test_Project

:D:D:D

Others doesn't make any sense with this thematic.;)

eliascom20
07-06-2009, 03:56 PM
For sure your problem is wrong turn.change immediately one phase if is 3phase motor or change running by starting in 1phase