Hi
All , i want to know that what is the procedure to check the thermostatic expansion valve
i have uninstalled the valve from the unit and i want to check that will it work after installation or not.
(danfoss 407c 7.5 ton)

Brian_UK
06-05-2009, 07:37 PM
Measure the superheat at design conditions.

modvalve
07-05-2009, 10:38 AM
Why do you want to check it if you have un-installed it it needs to be installed to check correct operation, you could always take it apart and check the internals for a rough idea

ateeq.baig
11-05-2009, 11:21 AM
Thans for the so suitabe idea

nike123
14-05-2009, 07:05 AM
If you already uninstalled TXV, than it is usually cheaper to install new one than install it back to found out that is faulty and then repeat all again. If you uninstalled it, change it!

D.D.KORANNE
14-05-2009, 12:31 PM
physical examination of valve might be of help such as damaged bulb, kinked capillary , bellow inside for visual crack if any . Function test only after you start system & observe design parameters.

ateeq.baig
15-05-2009, 11:12 AM
thanks All
for suggestions and the time to send

Yuri B.
03-06-2009, 04:43 PM
TEV and TXV is one and the same?

Gary
03-06-2009, 04:58 PM
TEV and TXV is one and the same?

Yes... Thermostatic EXpansion Valve

At one time, TXV was the more common abreviation, but over the years TEV seems to have become more common.

Yuri B.
03-06-2009, 05:02 PM
Hello Gary. May one accronym be in American usage, another in British? (only which where?)

Gary
03-06-2009, 05:05 PM
I have heard it both ways on both sides of the pond, but TEV seems to be far more commonly used outside of the USA.

Yuri B.
03-06-2009, 05:05 PM
Yes, thank you - TXV is rather the obsolete term.