I am getting following error code in 30GX 160 TR and 190 TR : Error Code No. 303, 14, 55, 20 & 50. I don't carrier manual with me, can anyone please provide me the details of these errors and solution for rectifiying the problem.

Brian_UK
01-04-2009, 06:57 PM
Have you tried the Carrier literature site.

http://eto.carrier.com/lit.asp

Scroll down the list for the 30GX

goshen
05-04-2009, 08:03 PM
303 hi press 55 no flow comp

udayam2008
10-04-2009, 05:45 PM
Unit tripping instantly while start up due to failure of oil pump on line

rakesh06
14-04-2009, 03:40 AM
hi well i thick that you has problem with the compressor board n can skip the board to do a test n i will give u most detail on the alarm code ok

serviceman
21-10-2009, 11:37 PM
DEAR
20,50,14,303 THE ALARMS ARE NOT IN THE MANUAL WITH RESPECT ME I NEED 55 ALA ALARM ALARM YOU SAY THAT APPEARS IF THE DRIVER COMFORTLINK ALARM AS OTHER FACTORS 55 are CCP or the module is damaged.

Gibbo
22-10-2009, 10:02 PM
There are 3 versions of this chiller, can you describe the chiller display that will identify the version so we can point you in the right direction regarding the manual.

goshen
23-10-2009, 01:10 PM
14 Discharge pressure transducer failure, circuit A Measured signal = 0V dc Circuit A shut down Automatic Defective transducer, wiring fault
15 Discharge pressure transducer failure, circuit B Measured signal = 0V dc Circuit B shut down Automatic

20 Oil pressure transducer failure, compressor B1 Measured signal = 0V dc Compressor B1 shut down Automatic Ditto



3xx Defect compressor B1 See CPM subcodes below See CPM subcodes below Manual