I have a 3PH AC motor 315 Kw that with equal voltages for each coils,amperes are diffrent(about 60A).
what causes are for this problem?

Electrocoolman
12-03-2009, 10:02 PM
Where are you measuring voltages?

On supply to fuses or contactor, or at motor terminals?

nike123
12-03-2009, 11:07 PM
If you measured voltage at motor terminals (as Electrocoolman suggested) than motor windings are damaged (partial winding short circuit).
Check insulation with megger.
http://www.biddlemegger.com/biddle/Stitch-new.pdf