I havn't got much experience on these units so anyway I have to recover a charge from a VRV system tomorrow.

Do I have to change any dip switches or other settings to force all valves open before I start recovering?

Cheers

Thermatech
21-02-2009, 12:08 PM
No special dip setting needed
Just connect recovery mc to both service valves at outdoor unit

cmac
21-02-2009, 12:40 PM
Nice one, thanks

1torr
21-02-2009, 07:44 PM
With everything powered up or off?

Thermatech
21-02-2009, 09:10 PM
On or off

Y series recover from both service valves. If LEV valves at indoor open or shut still get all the refrigerant out ok.

R2 series still get all the refrigerant out as BC box all solenoid valve pistons have bleed orifice which allow refrigerant recovery & evacuation even if indoor unit LEV valves are shut provided recover & evacuate from both service valves at outdoor unit.