View Full Version : Copeland Scroll Compressor



pjalchemist
17-01-2009, 02:49 AM
It's model ZR23K1-PFJN522

Single phase, 240v, 50z, 10.2A
R-22
Made 1994

This is going too cost the earth too run i know it but will it run okay on my house hold sparks or blow it?

Also im trying too find the full specs for it online but no luck at all with it!

Anyone able too help

Scramjetman
17-01-2009, 04:45 AM
I haven't seen other threads on this but I'm assuming its A/C that you are using it on.
Generally Coefficient of performance (COP) for an average A/C is about 2.5 - 3 which means that refrigeration power is approximately 2.5 - 3 times the kW of the input power in kW. At 240v and 10.2A, Watts = V x I ( 240v x 10.2A). Input power is 2.45kW. Lets work on the lower end of the efficiency and say that the COP is 2.5. Refig power= Input Power x COP (2.45kW x 2.5). Refrig power about 6.1kW.

If you can't find anything, this may get you started.

nike123
17-01-2009, 06:19 AM
Is this OK?;)
2646

2647

What is use for this compressor?

Brian_UK
17-01-2009, 11:04 PM
In answer to your question, check your kettle, it runs at higher amperage than that compressor.

You might need to run it on a separate circuit so that you can put a motor rated circuit breaker in line with it for starting purposes.

mekaniko5
16-02-2009, 07:25 AM
You can find this model's full specification at emersonclimate.com.
However, here is the full specification of that compressor. The correct model number is ZR23K1-PFJ.

K.R.Iyer
25-02-2009, 11:33 AM
At 240v and 10.2A, Watts = V x I ( 240v x 10.2A). Input power is 2.45kW.

You have missed mutiplying V x I by power factor - which for single phase compressor could be 0.85 to 0.9