Log in

View Full Version : one door up right problem



toes
11-01-2009, 03:39 PM
unit status:
134a suction 25 psi head 175
clean condensor, new evap fan , new tx valve, clear sight glass. running at 52 degress to 47 dgrees
tx valve is one turn away from wide open

Any ideas?

multisync
11-01-2009, 03:53 PM
Gary will be along soon with a list of measurements you really should take before posting!

In the meantime,Shut the valve down 1 turn and see.

Gary
11-01-2009, 04:00 PM
Why is the TXV wide open?

Gary
11-01-2009, 04:01 PM
Gary will be along soon with a list of measurements you really should take before posting!

In the meantime,Shut the valve down 1 turn and see.

I get tired of typing the list and nobody provides the measurements anyway.

Brian_UK
11-01-2009, 04:49 PM
Put the valve back to its correct setting and then give us a set of readings after it has stabilized.