View Full Version : foster ps 500 lt r404a
shrewey
05-12-2008, 05:00 PM
hi there everyone.. im currently working on a fault with a fosters ps 500lt 404a, both the con and evap fans are working,but the freezer is not freezing,it is staying at 22 oc. my work mate will be pressure testing it monday, for a loss of refrigerate. any ideas what the problem could be,if its not a leak?
thanks mark...
ps.. im a spark who works with a air con engineer..
Comp not pumping/ blockage in fridge circuit, assuming condenser fan is running and condenser is clear, check defrost heaters are not stuck on.
You really should be fitting your manifold set and anylising the system before you do anything.
Let us know how you get on
Dr._Fleck
05-12-2008, 06:06 PM
The little bi metallic clicky thing has gone open circuit on the compressor mate, you need a new one.... i am good cc
shrewey
05-12-2008, 06:23 PM
thanks for your help,i will relay that info to my work mate... and will let you know the outcome..
I do assume the compressor is running
PP
taz24
05-12-2008, 07:34 PM
I do assume the compressor is running
PP
Not if Dr Fleck is right, its the little clicky thingy :D
The little bi metallic clicky thing has gone open circuit on the compressor mate, you need a new one.... i am good cc
Your the man :p
taz
.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.