Log in

View Full Version : Cek leakage in evaporator



Cewek ITS
14-10-2008, 10:37 AM
I have new an evaporator using TEV externally equallizer intalled in this unit. I want to test leakage using gas with high pressure about 10 bar and using detergent water. I will fill the gas from inlet TEV. Is it permitted ? Is TEV valve in open orifice or closed orifice in the ambient temperature. I buy TEV from danfoss type TE N 2. I'm worried the gas can not pass through TEV and I can not check leakage in the evaporator side and pipe externally equalizer that is connected in the out of evaporator tube because there is no pressure inside tube. Please need your advice

BR,
Yudha

TRASH101
14-10-2008, 11:21 AM
Hello Cewek

The gas will pass through the TEV ok but it will be a little slow.

TE2 N is for r134a so why 10 bar test pressure for leakage. Please check manufacturer recommendations for maximum.

here is a link for the TE2

http://www.danfoss.com/NR/rdonlyres/CA5E4257-4F6B-4F41-A268-8CB4FE6874DD/0/PFA00A102.pdf

sedgy
24-10-2008, 11:54 PM
about the 10 bar of 134a I allways thought we used ofn for oressure testing

taz24
25-10-2008, 09:16 PM
about the 10 bar of 134a I allways thought we used ofn for oressure testing


With 134a you can pressure test to about 13bar
and yes pressure testing is done with OFN but sometimes
if the leak is small and hard to find then it has been known
to use some Helium because of the molecular size of the
134a.


Cheers taz.