View Full Version : uneven evap flooding



grapple
20-08-2008, 09:36 PM
working on hubbard cellar cooling. ext equalizing tev distibutor with three tails. top section only 2 bends flooding. middle section 3 or 4 bends, bottom section flooding to comp. any light welcome to be shed.

Ponca Dave
22-08-2008, 03:10 AM
Replace the TX Valve.

Chunk
22-08-2008, 05:40 PM
A couple of causes for you to mull over.

1.Blocked or partially restricted distributor.

2.Incorrectly sized txv orifice.

3.Oil logged evaporator.

I would go for number 2.:)just as a guess.