View Full Version : Parker A4AS Valve Issue



brian_chapin
30-07-2008, 12:07 PM
Parker A4AS valve warning:

I recently became aware of an incident that had occured with the A4AS pressure regulator. The valves larger than 1 1/4" are bolted, so this problem only exists on the smaller valves.

It seems that in very rare circumstances, the seal cap covering the manually opening stem can corrode fast to the valve bottom cap. If this valve has been insulated, the technician may think they are loosening the cap when they are in fact taking the entire bottom of the valve off.

This leads to a very unpleasant suprise and a significant refrigerant release. This has actually happened to two technicians I know. Simply removing the insulation to the point where you can see what parts are turning is all that is needed to avoid this issue.

Of course, the occasional exercise of the valve and application of anti-seize is always a good idea too.

Grizzly
03-08-2008, 07:58 PM
Thanks for the info Brian.
Sadly there are other Manufacturers Valves out there with similar faults.
So as you point out it has become prudent.
Nowadays to expose more than the Valve Cap Head prior to removal.
cheers Steve.

pweng
27-08-2008, 11:23 AM
I need operating instructions for an A4AS regulating valve please

keepitcool
27-08-2008, 11:31 AM
Try this.

http://www.parker.com/portal/site/PARKER/menuitem.734d2913eb3c11da13576f849420d1ca/?

vgnextoid=d195f87357e28110VgnVCM10000048021dacRCRD&vgnextfmt=default&division=9b17981ef31a0110VgnVCM10000048021dacRCRD&literaturetype=Bulletins&searchAttr=searchResult&languages=EN&parentCh=Division#results

keepitcool
27-08-2008, 11:34 AM
Sorry, link did not come out right.

Mark Selby
02-09-2008, 12:08 AM
this problem can be fixed. Anytime we install valves we dress all threads with anti sieze

CHIEF DELPAC
03-09-2008, 04:34 PM
I have the same problem with 1 inch and smaller valves in NH3 service . Isolating valves and hand expansion valves have a screw in bonnet. I have had these valves start to unscrew the bonnet rather than the valve spindle.

These valves cannot be used on new installations. But there are lots of these valves in older refrigeration engine rooms.

Iceehot
05-09-2008, 02:23 AM
Ran into a left-hand threaded bonnet last week, pulled new valve from stock and it was right-hand threaded bonnet! Two different brandnames. Be very careful of any threaded bonnet.

Loafa
16-02-2009, 07:41 AM
Hi Pweng if you email me plougher@slingshot.co.nz I will send you a manual