Log in

View Full Version : Charging 410a systems



HvacKid
04-07-2008, 04:04 AM
I know when charging a 410 system you have to add the charge as a liquid into the suction side. I purchased a Kwik Charge to aid me in this. My question is does the Bottle of 410 have to be inverted (upside down) ?

refmech
04-07-2008, 03:07 PM
you need to read/look at your can. some have a pick-up tube some dont.:)

bethlehemtech
04-07-2008, 03:26 PM
most refrigerant cylinders have to be inverted to charge as a liquid. If it is a recovery cylinder then it has a liquid service port. Be sure that if using recovered refrigerant that it does not contain non-condensables.

2007eng
05-07-2008, 01:58 PM
Most R410a cylinders have a pick-up tube (syphon) so you don't need to inverted it (upside down) depending on the cylinder type. Be sure that the cylinder have a syphon then proceed without inverting, else= invert the cylinder(upside down).

There are some good informations about this subject in the attachments.

marc5180
12-07-2008, 12:32 PM
If charging as a liquid i always turn the cylinder upside down. I was told that when the bottle is the correct way the dip tube doesn't go all the way down to the bottom so when there isn't much left in your bottle and you think your chaging as a liquid, you could actually be charging as a vapour. For this reson if you turn the bottle upside down you know you will have liquid for sure.

marc5180
12-07-2008, 12:34 PM
Double post sorry

airconadam
12-07-2008, 10:58 PM
ido as posted by marc just what i got taught and is a habit now thanks alot

adam

sinewave
13-07-2008, 06:49 PM
For this reson if you turn the bottle upside down you know you will have liquid for sure.


Only as long as you remember swap over to the Blue Gas outlet and not the Red Liquid valve. :cool:

marc5180
30-07-2008, 05:58 PM
Only as long as you remember swap over to the Blue Gas outlet and not the Red Liquid valve. :cool:
I always put onto the blue/vapour, then invert the bottle

Peter_1
30-07-2008, 06:25 PM
Most bottles we have only have 1 valve, so you can't choose if you want to invert it or not.
As others said, it depends on the type of the cylinder.