View Full Version : assab ultra 85 ???



thebigcheese
27-06-2008, 07:47 PM
anyone outhere look after any assab ultra 85 low temp units.... need to no the correct charge for 404a on first stage

marc5180
05-07-2008, 05:11 PM
Doesn't look like it thebigcheese

thebigcheese
09-07-2008, 05:17 PM
ino fs this thing is doing my nut in its been ongoing now for around 4 weeks

marc5180
30-07-2008, 05:59 PM
Silly question but have you searched the net?

thebigcheese
30-07-2008, 10:27 PM
got it sorted anyway had abit of guesstomation and its at -75 again so il leave it at that

richardb14
18-02-2009, 07:29 PM
ah the old TAS cabinets!! they used to manufacture the same cabinet for peter swan.

there is nothing set in stone for these cabinets, the pressures are all different. they usually run about 5psi suction pressure on the first stage, 2nd stage is R170, watch out for waxing inside the capillary on first stage its a common problem, you will need to change the capillary. in fact maybe that is your problem

richardb14
18-02-2009, 07:31 PM
just another point to add - they dont work too well on R404A, but R507 works ok.

thebigcheese
24-02-2009, 09:10 PM
yea mate capillary was bad it blocked a spin drier within two hours... its been awile now anyway so fingers crossed